Results 1 to 4 of 4
  1. #1
    Join Date
    Aug 2001
    Posts
    130
    Post Likes

    Hmm

    (System is straight cool, 10KW 1-stage heat.) Just installed this variable speed air handler with a matching 12-SEER Am Standard condensing unit. All works well in cooling mode (soft start, 1/2 speed for 7 1/2 minutes, etc.)but air handler will not start in heat mode. Wired correctly, has 24-volts at the W-1 terminal, but the heat contactor will not pull in and the blower motor sits idle. Passes all tests using the factory "Trouble Shooter" circuit board and 4-wire test cable, and all connections/connectors appear to be well made. When a jumper is momentarily connected from the common side of the heat contactor to the common on the low-voltage terminal board, the contactor pulls in (but the blower remains idle). Anyone had a similar problem...fix?
    Thanks,
    Mike

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    38,940
    Post Likes
    Regular Trane air handlers require the stat to bring on G with a call for heat. Maybe this one does too. Someone pointed out a while back that if the blower isn't energized, a relay breaks W1 between the terminal strip & the contactor.

  3. #3
    Join Date
    Feb 2005
    Location
    Alabama
    Posts
    534
    Post Likes
    Bald is right, need to have G connected from AH to stat. My only question is why you would want a variable speed AH with a straight cool system.
    "If you can't fix it, don't break it."

  4. #4
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,868
    Post Likes
    These guys are right in telling you that G needs to come on with W and is normally done with a trane stat or a stat that you can setup for electric heat this way by changing a setting. Common for the heat contactor is switched through the blower control.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.