nitrogen to purge oil?
Question for you guys that deal with chillers out there often:
I have an r-22 acme 150 ton chiller that is in our lab, we use it for students to get some time on a chiller. Problem is, the last group that went through filled it so full of oil that it is coming out the access port. The drain plug is positioned in such a way that it is a real pita to drain without making a mess. I have all the pieces needed to make a drain tube down with a shutoff so that we can simply hook a hose up and drain it easily, but i still have a ton of extra oil in the system.
My question is.. can i use a bit of nitrogen (this doesn't have a low pressure disc) to pressurize the compressor while isolated (already recovered refrigerant from the oil) to essentially pump the oil out into a vessel?
thanks in advance for your time, guys.
-
01-25-2011, 12:26 PM #2
Professional Member
- Join Date
- Jan 2011
- Location
- Russellville, Alabama
- Posts
- 26
I think if it were me, i'd be more inclined to pull a vacuum on a small vessel of some kind that isn't being used and has a good drain location on it, then use a small hose with a shutoff valve connected to it to submerge in the lowest point of the chiller. It'll remove oil very well....
-
01-25-2011, 04:09 PM #3
fwiw I'm far from a chiller guy, I'm jus a grunt that works on a little of everything, and sometimes even fix it haha.
I'd second the vacuum idea too. Should be a more controllable, less messy and more proficient way to do it.
Their mistake is actually a good one, because at some point they will run into this in the field and have to do this."If you call that hard work, a koalas life would look heroic."
VETO PRO PAC, The Official Tool Bag of HVAC-Talk.com
Testo... you guys rule!
-
01-25-2011, 06:42 PM #4
why don't you pump it down, recover the refrigerant out of the compressor body, bringing it into a vacuum, and swap out the plug with a valve on the fly?
\m/
-
01-26-2011, 07:49 AM #5
Professional Member
- Join Date
- Dec 2010
- Location
- Eaton Rapids, Mi
- Posts
- 254
well, it was pumped down and recovered, but i don't see the point of pulling a vac if i'm going to swap the plug.. wouldn't it make more sense to swap the plug and THEN pull a vac?
turns out there was no need to remove any oil, there was 10 or so pounds of refrigerant that migrated to the oil. removed that, and the oil level was actually a little low.
I was just curious if you could pressurize oil safely into a recovery tank with a vac on it. The unit in question has a service port on the oil fill hole, and it'd be really easy to put a hose on there.
Thanks for the suggestions, though!
-
01-26-2011, 08:36 AM #6
Professional Member
- Join Date
- May 2008
- Location
- Central Pennsylvania
- Posts
- 413
-
01-26-2011, 09:59 AM #7
Professional Member
- Join Date
- Dec 2010
- Location
- Eaton Rapids, Mi
- Posts
- 254
-
01-26-2011, 11:04 AM #8
Professional Member
- Join Date
- May 2008
- Location
- Central Pennsylvania
- Posts
- 413
-
01-26-2011, 07:43 PM #9
I also recommend installing a service valve in place of the drain plug. It will come in so handy for things like sampling or adjusting the level. This would be a good teaching point on oil management and the various conditions that cause the oil to take off out into the system.
However, I refuse to use Leak-Lok, and would use only the Loc-Tite refrigerant thread sealer for something like this. I have seen way too much misuse of Leak-Lok locally, like a highly touted contractor whose installer used it on flare fittings, making up line sets. I use only refrigeration oil on flare fittings. The correct sized wrenches and a good tightening.
Also bone up on the EPA regs regarding adding and or removing compressor oil.God Bless the USA
-
01-26-2011, 08:36 PM #10
Heavy's trick will work very well I have done a charging valve on a large low pressure chiller without losing a drop of freon just have to be quick.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
01-26-2011, 08:57 PM #11
Professional Member
- Join Date
- Dec 2010
- Location
- Eaton Rapids, Mi
- Posts
- 254
I am going to run a 45 off the outlet, and angle that down with a NPT to flare fitting so we can attach a copper line, or a hose to it for access. I plan on putting in a service valve as well. Seems like the easiest way to add access to it.
could you elaborate on this? i'm not aware of any regulations regarding removing oil? do you mean regulations regarding disposal?