    Anyone have a K factor chart for VCW boxes?

  2. #2
    Join Date
    Nov 2003
    Location
    Boston
    Posts
    600
    I have a list of Flow Coefficients from a Siemens manual that lists a Trane box as 0.66.
    It does not list model numbers and I don't know how old the list is.
    Hope that helped.

  3. #3
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    3,642
    Sys is this the older boxes or the newer ones?

    I have a IOM manual on these model boxes in Pdf form and at the beginning it says for air balancing instructions see
    EA10_IOM2-E, the manual I have doesnt have the K factor but the one I just listed should.
    Dad's Hideout The online mancave for dads

  4. #4
    Join Date
    Mar 2003
    Location
    Washington,NJ
    Posts
    504
    If you know the inlet size of the box, regardless of manufacturer, the number will be the same. A 10" box is a 10" box, ask any balancer.

  5. #5
    Join Date
    May 2002
    Posts
    9,564
    ...you know you say that and they all end up being a little different. What's the reason is what I want to really know.

  6. #6
    Join Date
    Mar 2003
    Location
    Washington,NJ
    Posts
    504
    Even if they are the slightest bit different, your balancer should give you the proper multiplier to compensate for that, but I know what your talkin about!! I'll check my online info for the Trane VCW box and get you the correct info, hey man, don't you ever sleep? Bacnet rules!!

  7. #7
    Join Date
    May 2002
    Posts
    9,564
    ... too busy fighting the ASHRAE BACnetter propaganda...

    if somebody would send over a cape I'd be set.

  8. #8
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    3,642
    Sys, see my post above, that should be the manual you need
    Dad's Hideout The online mancave for dads

  9. #9
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,474
    Originally posted by sysint
    ... too busy fighting the ASHRAE BACnetter propaganda...

    if somebody would send over a cape I'd be set.
    Keep up the good fight, we need you!
    "Profit is not the legitimate purpose of business. The legitimate purpose of business is to provide a product or service that people need and do it so well that it's profitable."

    James Rouse

  10. #10
    Join Date
    Aug 2003
    Posts
    422

    Sometimes K factors are....

    ....the amount of CFM a box will deliver at 1 inch of differentialpressure.

  11. #11
    Join Date
    Apr 2007
    Location
    San Diego, CA
    Posts
    1,249
    reviving this thread... I was looking for the same thing, found this IOM dated June 2006. See page 32 for an updated pressure differential vs cfm flow chart with actual box sizes.
    http://www.trane.com/Commercial/Uplo...av_unitiom.pdf

  12. #12
    Join Date
    Sep 2006
    Location
    Alaska
    Posts
    406

    Trane K Factors

    Duct Size Area K Factor
    5 .14 3.27
    6 .20 2.65
    8 .35 2.44
    10 .55 2.30
    12 .79 2.30
    14 1.07 2.30
    16 1.40 2.27

    This is the chart I have for Trane, hope it helps!!!!

  13. #13
    Join Date
    Apr 2007
    Location
    San Diego, CA
    Posts
    1,249
    HW spudders ask for the k-factors as box CFM @ 1 in w.c.

    What's the conversion from your method?