    36
    I am installing a Trane highboy oil furnace. How much clearance from the top of the furnace do I need for the evap coil. I believe at least 4 inches.or the coil could melt.. is this true?

    Thanks

  2. #2
    Join Date
    Feb 2004
    Location
    Maine
    Posts
    483
    What does the install manual say?

  3. #3
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,209
    Hopefully this is an upflow, most install manuals say 2" to combustibles, most coils have a plastic pan. So 4" would be safe. Alway's consult install instructions.
    Proud supporter of Springfield Millers and Oregon Ducks.

  4. #4
    I always go 6 inches to be on the safe side. Oil is so much more hotter than gas as we all know.Regards HH.

  5. #5
    Join Date
    Sep 2002
    Posts
    237
    Use a coil with a metal drain pan.. we always use them on oil with no problems

  6. #6
    Join Date
    Sep 2004
    Posts
    654
    I've installed A-coils no more than 4" from the top of the furnace and no problems to date. Heat exchanger is probably at least 2" below that, so 4" off the top of the furnace is plenty.