    Another hydronic geothermal job

    Just finished this job and wanted to get a few pics up. Still waiting for Mech insulation, I will post updated pics when done. This is a fire station with 3 infloor heat zones and will have chilled water cooling later on from the 2- 10 ton heat pumps.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  2. #2
    Join Date
    Feb 2005
    Location
    L.I. NY
    Posts
    129
    Post Likes
    Looks good, the only thing I do not like is in the middle photo the back wall.

    The 2 center lines straight thru the tee's will flow more that the outside lines that are on the side outlets of the tee's.

  3. #3
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    how do you like the crimper?

    had any issues with it?
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  4. #4
    Join Date
    Jul 2008
    Location
    Poestenkill, NY
    Posts
    769
    Post Likes
    Quote Originally Posted by kevink1955 View Post
    Looks good, the only thing I do not like is in the middle photo the back wall.

    The 2 center lines straight thru the tee's will flow more that the outside lines that are on the side outlets of the tee's.
    I think there are circuit setters, moot point if so...

  5. #5
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by kevink1955 View Post
    Looks good, the only thing I do not like is in the middle photo the back wall.

    The 2 center lines straight thru the tee's will flow more that the outside lines that are on the side outlets of the tee's.
    Good eye, but I've got that covered. It's reverse return piped so that circuit #1 goes straight out but not straight back in. Circuit #2 is hooked up to the other side going straight back in so it's equal for both.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  6. #6
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by larobj63 View Post
    I think there are circuit setters, moot point if so...
    See response to kevik about reverse return piping. Also no need for circuit setters as both circuits are identical footages nearly down to the inch. I didn't want to complicate it and add pressure drop when not necassary. There are PT ports on all 4 pipes of both circuits we checked pressure drop and flow is a spot on match. Thank you for responding.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  7. #7
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    Is that diamond plate behind the controls?

  8. #8
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter

    Smile

    Quote Originally Posted by dandyme View Post
    how do you like the crimper?

    had any issues with it?
    The propress tool has been one of the best investments ever. Looking back at all the jobs like this we used to do by soldering I can't believe all the time I'll never get back. I have never had a leaking problem other than human error such as pipe not in far enough or in crooked and snagged the oring even that only a couple times. I just hope the connections outlast me.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  9. #9
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by ascj View Post
    Is that diamond plate behind the controls?
    Yes sir, 16 ga aluminum. Just for looks.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  10. #10
    Join Date
    Sep 2008
    Posts
    697
    Post Likes
    I know squat about geo but the piping sure looks purdy....nice touch with the diamond plate haven't seen that b4.

  11. #11
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    Wow, I'm impressed with that!

  12. #12
    Join Date
    Apr 2009
    Location
    Lancaster,PA
    Posts
    25
    Post Likes
    Very clean pipe work......Nice Job

  13. #13
    Join Date
    Jul 2008
    Location
    Poestenkill, NY
    Posts
    769
    Post Likes
    Quote Originally Posted by yorkguy View Post
    See response to kevik about reverse return piping. Also no need for circuit setters as both circuits are identical footages nearly down to the inch. I didn't want to complicate it and add pressure drop when not necassary. There are PT ports on all 4 pipes of both circuits we checked pressure drop and flow is a spot on match. Thank you for responding.
    Pretty clever - I like how you did that.

    Depending on how long the circuits are (read- if they are very long and/or high head) - using the run or bull of the Tees won't effect flow in one circuit versus the other much anyhow. But, that being said, you thought about it and did the smart play by simply reversing the return path, so I'll just shut up. lol

  14. #14
    Join Date
    Jan 2008
    Location
    Calgary AB
    Posts
    227
    Post Likes
    Damn that looks sexy and clean

  15. #15
    Join Date
    Jan 2011
    Location
    TN
    Posts
    93
    Post Likes
    very nice if only every new install looked this good

  16. #16
    Join Date
    Nov 2008
    Location
    Paradise
    Posts
    865
    Post Likes
    Thats got be some of the nicest work I've seen in awhile.
    Radiant heat threw out the house, and hot water? What Style house and square ft?

  17. #17
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by Vinpadalino View Post
    Thats got be some of the nicest work I've seen in awhile.
    Radiant heat threw out the house, and hot water? What Style house and square ft?
    Its a fire station with radiant floors throughout. Upper levels wii be forced air addeed later with air handlers and water coils
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  18. #18
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter
    Pipe is all insulated and labled now. Here is the finished product.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

  19. #19
    Join Date
    Dec 2010
    Location
    Palm Beach,Fl.
    Posts
    1,091
    Post Likes
    Pure 100% Craftsmanship. Beautiful work sir!

  20. #20
    Join Date
    Jul 2006
    Location
    St.Paul, MN
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by SoFlaDave View Post
    Pure 100% Craftsmanship. Beautiful work sir!
    Thank you very much, I've also started a new thread with a couple addiional pics not shown here but otherwise the same.
    Remember, some poor fool has to work on what you install someday, and it might even be you.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •