Results 1 to 12 of 12
  1. #1
    Join Date
    Sep 2004
    Posts
    62
    Post Likes
    Does anyone know what the wiring scheme with resistors is to convert a 4-20 ma signal to a 135 ohm slide wire control to control a 135 Ohm actuator. I know a converter can be bought but I would like to avoid that and simply wire with the needed resistors. Does anyone have this wiring schematic already done. I know someone has done it but it is not sold by the manufacters because it is a cheap solution. A few dollars in resistors.

    Thanks

    Jack

  2. #2
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,250
    Post Likes
    Good Luck!!!!

  3. #3
    Join Date
    Mar 2003
    Posts
    7,381
    Post Likes
    check the lit on your particular controller, some can be easily configured to do this internally.

  4. #4
    Join Date
    Jan 2004
    Posts
    44
    Post Likes
    depending on actuator brand, honeywell and johnson make signal adapters
    Union Yes

  5. #5
    Join Date
    Feb 2005
    Posts
    1,463
    Post Likes
    To make it accurate, you will need many steps hence many resistor combinations and stepper.
    May want to save yourself the headache and look at:
    http://www.act-solutions.com/pdfs/drn4/drn4_spec.pdf

  6. #6
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,913
    Post Likes
    Checkout a NEPTRONIC Ki-135 Transducer

    Converts 0-10VDC , 2-10VDC , 0-5VDC and 4-20MA to 0 - 135 Ohms

    It is a bit BULKY in size( 3.5" H X 2.2" W x 3.5" D ) but does a nice quick job , uses a 11 pin relay socket

  7. #7
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    It's called a DRN, from honeywell

  8. #8
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,028
    Post Likes
    Theres a manual from Honeywell that tells you how to convert using resistors, I have a copy somewheres, what are you trying to do?

    If this is on a modutrol you can buy a module for less than 100 dollars from Honeywell that will convert slidewire to 4 to 20, also Kele sells different items that do this too
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  9. #9
    Join Date
    Sep 2004
    Posts
    62
    Post Likes
    Thread Starter
    OK, thanks for the comments I do have a solution and I will send it (The Schematic) when I get done with the job. Just wondered if anyone had a better solution. Mine costs less than 5 bucks in resistors.

  10. #10
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    is it a 232 and two 66 ohm resistors ?

  11. #11
    Join Date
    Sep 2004
    Posts
    62
    Post Likes
    Thread Starter
    Additional comments: a 135 Ohm slide wire controller requardless of make or model should be able to be controlled with a 4-20 ma control signal and two properly sized resistors. Keep in mind the ma signal varies the resistors don't have to vary. Somebody should be able to figure this one out.

    You may need to use the standard 300 Ohm pot that is on a lot of these slide wire controllers to adjust and fine tune the controller action of the dampers.

    I'll let you know how I did it after I get done with the job. I'm working on the old M955 Honeywell Actuators.

  12. #12
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    i have never trie dto figured it out the DRN is about 80 bucks, and will control a lot better JMHO

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.