Results 1 to 13 of 29
Thread: delta T ?
04-05-2005, 08:33 PM #1
- Nov 2004
- CA
- 236
on a Residential A/C
Between me an my fellow coleage we have that discussion.
I say 20-25 F
he says 10-15 F.
My argument is: Temp. after Evap. is approx. 50 F - and in the Return is 75 F.
Help me out - who is right ?
04-05-2005, 08:40 PM #2
- Apr 2002
- 1,471
20 to 25 is right ... if you live in the desert then lower delta t has some merit
04-05-2005, 08:40 PM #3
Professional Member*
- Jul 2001
- Anderson,SC
- 882
If you subtract 50 from 75, your right.
Now if you are asking what is the correct DT you need a chart and WB temp. Most will be happy with DT of 20. Your fan speed is the biggest factor on how much heat is being removed from the air.
STUD
04-05-2005, 08:45 PM #4
- Jul 2001
- 40
I am a little confused...isn't this a web site for professionals in the field. The very question indicates the author knows nothing about HVAC...
Just my opinion.
04-05-2005, 08:57 PM #5
- Apr 2002
- 1,471
hey i know plenty of pros who arent
04-05-2005, 09:03 PM #6
- Nov 2004
- CA
- 236
umd,
what is your opinion - if you have one ?
I am sure you are a Super Professional, that is why I humbly ask you for your opinion.
Let's see what are you up to? C'mon be a man, say it ...
04-05-2005, 09:08 PM #7
Banned
- Mar 2004
- Gone
- 5,340
The man asked a specific question pertaining to Delta T, and showed where he was getting the temperatures to verify this. I think he knows a little more than just nothing, dont you?Originally posted by umd
Just my opinion.
04-05-2005, 09:09 PM #8
this guy is not a pro but reasonable question
depending on blower speed
18 to 25 is good but super heat and subcool is the best way to check
04-05-2005, 09:15 PM #9
- Nov 2004
- CA
- 236
madeinusa,
I took the readings right after the Evap. Coil, let's say 3-5 " on the Supply - and 12-24" before filter on the Return.
04-05-2005, 09:28 PM #10
20 degree TD
FILL OUT YOUR PROFILE!!
04-05-2005, 09:30 PM #11
- Apr 2004
- Niantic, Illinois
- 545
The guy is in the learning process. Wow, switch to decaf.Originally posted by umd
Just my opinion.
04-05-2005, 09:43 PM #12
- Jul 2001
- 40
Ok, I'll take the bait...The dry bulb delta T across the evap coil will be a function of the amount of sensible heat removal from the airstream and the amount of air going across the coil. Now if you were only doing sensible coiling (not removing any moisture) the formula would look like this: BTU/HR(sensible)=CFM X1.08 X DELTA T. Unfortunately in the real world you are usually removing some latent heat which is not measurable by dry bulb temperature. To accurately predict the delta T, you would need to know the wet bulb temperature of the entering and leaving air. You would also need to know the airflow across the coil. Using a psychrometric chart you could predict what your delta T would be by calculating the actual enthalpy per pound of heat in your entering and leaving air and use the formula: BTU/HR (total)= CFM X 4.5 X DELTA H (actual heat content of air).
The bottom line is this: your delta T could be anywhere from 10 to 20 degrees depending on the amount moisture in the air and the amount of air going across your coil. Low humidity equals high delta T; high humidity equals low delta T.
Sorry if you were offended.
04-05-2005, 10:02 PM #13
- Nov 2004
- CA
- 236
umd,
I really thank you for your answer.
"Offended" - not.
a bit ticked-off by your first reply - yes !
Not anymore.
Thank you, again.