Results 1 to 11 of 11
  1. #1
    Join Date
    Apr 2005
    Location
    SWFLA
    Posts
    4
    Post Likes
    I am having my two A/C units replaced with two 2-ton Infinity systems. In order to get more air into a couple of rooms that were always hotter with the old system, my HVAC tech is replacing the current ductwork going into those rooms with larger ducts, running them directly from the air handler to the registers. The concern I have is that he is not replacing the registers, and is running the larger 7-inch ducts into the existing 5-inches registers, joining 7" into the 5" near the registers. I know that this is not the right way of doing it, but should I be concerned with this set-up?

    Any input would be greatly appreciated.

    Thanks

  2. #2
    Join Date
    Apr 2004
    Location
    Niantic, Illinois
    Posts
    545
    Post Likes
    That's not necessarily wrong. The larger duct will carry a larger volume of air to the end of the run. Where it reduces, that volume of air will increase in velocity causing greater throw into the room. This is based on a relatively balanced system that is working at the correct static pressure. Basicly a properly sized duct system. If the larger duct doesn't have enough air feeding it, it will still have poor airflow.

  3. #3
    Join Date
    Apr 2002
    Posts
    1,471
    Post Likes
    registers can be restrive ... we cant tell from here

  4. #4
    Join Date
    Mar 2005
    Posts
    17
    Post Likes

    Whoosh

    Wouldn't reducing from 7" to 5" right at the register boot create a bit of noise? Or at the least, restrict the air flow substantially? My ductilator seems to think so. berad's point about the size of the trunkline is very valid also.
    Run a load on the room, measure how much air you're getting and compare it to what the load says you should have. Don't let your guy guess!(It kinda sounds to me like he might be.)

    Just one man's humble opinion.
    Regards,
    Jim

  5. #5
    Join Date
    Apr 2002
    Posts
    1,471
    Post Likes
    yes restriction equals noise ... i would enlarge it for noise reduction

  6. #6
    Join Date
    May 2000
    Posts
    3,914
    Post Likes

    Arrow 7-5 ...

    Increasing the 5" to 7" is going to increase the air flow reaching those registers. Nobody should be worrying about velocity and noise on a 7" duct run reduced to 5" at the boot, at best it will improve the throw of the register. Increasing the boot may actually dimish the throw the 7" provides to the 5" ....

    I would not worry about noise of 160 cfm @ an estimated 600 FPM, the old 5" under perfect conditions provided 70 cfm @ 500 FPM not a real noticable difference.... An improvement but nothing to worry about...
    AllTemp Heating & Cooling

  7. #7
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    It could be very noisey or not,it all depends on what the 5"X?" register is designed to handle.

    They could/should be installing dampers at the takeoffs of those new runs to prevent over feeding those rooms.


    Best method is a complete ManJ and Man. D,and redesign the duct system.Note I said redesign,that doesn't mean rip it ou and start over.

    Chances are ,With Dampers ,you only needed a little more cfms,and it will work out okay,not prefect ,but a big improvemnet.

  8. #8
    Join Date
    Apr 2005
    Location
    SWFLA
    Posts
    4
    Post Likes
    Thank you everyone for your replies. It has provided me some clarification from both sides; no problem vs. more noise. I will ask the HVAC designer to re-think this installation.

  9. #9
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    the proper way to do it is run a trunk line with the correct cfms and then run short flex runs off it
    flex just adds to the static pressure of the system
    the reducers wont hurt any thing but be a little noiser
    running flex from the pleumun i disagree with

  10. #10
    Join Date
    Sep 2003
    Location
    McKinney, TX
    Posts
    471
    Post Likes
    If you trust the contractor, go with his recommendation. Its its screwed up and he is somewhat respectable, he will fix it. If there is any significant duct problems though, the infinity control will tell on them.

  11. #11
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    He's right ,no need to rip out the trinkline.Depending on the type of trunkline,a second trunkline to the area with low air flow may be a better choice then branchs coming off the plenum.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.