  1. #1
    Join Date
    Aug 2007
    Posts
    28

    Trane ignitor voltage

    I have a customer with a Trane gas furnace model# TUY100R9V4W5. I believe it was installed in 2005. They have had to have the ignitor replaced 3 times already. The first time I talked to Trane tech support I could not get a lot of information out of them other than they have changed the part number for the ignitor three times. I take that he was implying that they are just defective ignitors. The guy at our Trane supplier said that the boards on these particular models step down the voltage to the ignitor to 80VAC, and they have found some boards that fail to do this and thus send too much voltage to the ignitor, causing premature failure. I recently checked this out for the customer (I am not the one who did any of the repairs previously, just following up for them to try and resolve this issue) and found that the voltage to the ignitor fluctuates between 86VAC and 121VAC. I have a Fieldpiece multimeter that updates about every second, and the readings look like 86...94...121...86...94...121...etc, the entire time the ignitor is energized. At this point I am definitely leaning towards replacing the board (they have 10 year parts). I can't imagine these readings would be normal. I will be talking to tech support again on Monday morning but I wanted to throw this out here to see what any of you Trane experts think. I work for a Carrier and Lennox dealer and I just don't see a lot of Trane furnaces, and have never run into this problem.

  2. #2
    Join Date
    May 2005
    Location
    Western Kansas
    Posts
    267
    Not familiar with your meter, but if it isn't an analog, I'd recommend trying one before you condemn the board.

  3. #3
    Join Date
    Aug 2007
    Posts
    28
    It's a digital meter model HS36. I have used it for 3.5 years and have never had an AC voltage reading that fluctuated more than a couple tenths of a volt. I guess I could try an analog meter (after I dust it off hehe) but I am not sure it would give me any better info.

  4. #4
    Join Date
    May 2005
    Location
    Western Kansas
    Posts
    267
    I've just found reading voltages off of boards are totally different from putting them on two wires to see if you have high voltage. I see fluctuation with a digital that I don't see with the analog. I carry both. Might not be the problem, but when you don't see a constant voltage, eliminate the guessing with an analog, IMO.

  5. #5
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,921
    Twilly has solution.
    No Heat No Cool You need Action Fast

  6. #6
    Join Date
    Sep 2009
    Location
    Covington, KY
    Posts
    159
    Tell us about your solution Twilly!

  7. #7
    Join Date
    Aug 2007
    Posts
    28
    Yes, I'm all ears Twilly!

  8. #8
    Join Date
    Oct 2007
    Location
    Central New Jersey
    Posts
    33
    I've had readings like that when the igniter is not plugged into the circuit. I use the Fluke 87 meter. Are these readings with the igniter unplugged? It should read 80 volts with the igniter in the circuit. Anything over 80 volts will kill the igniter sooner.

  9. #9
    From what I remember from a Trane training class a year or so ago, The more recent boards with nitride ignitors "learn" what minimum voltage needs to be applied to the ignitor to get proper ignition to not wear the ignitor out prematurely. I think the boards may also be "chopping" the power to achive these voltages which would show up better on an analog meter. This may be normal. You may want to also check the quality of the incoming 115 VAC as well as the ground.

  10. #10
    Join Date
    Aug 2007
    Posts
    28
    Quote Originally Posted by Ghostrider67 View Post
    I've had readings like that when the igniter is not plugged into the circuit. I use the Fluke 87 meter. Are these readings with the igniter unplugged? It should read 80 volts with the igniter in the circuit. Anything over 80 volts will kill the igniter sooner.
    Ya, the ignitor was plugged in. I just pushed my meter leads into the back of the plug to the board. So, you have measured the voltage in this situation before, and it should be reading a constant 80VAC?

  11. #11
    Join Date
    Aug 2007
    Posts
    28
    Quote Originally Posted by bill_irwin32 View Post
    From what I remember from a Trane training class a year or so ago, The more recent boards with nitride ignitors "learn" what minimum voltage needs to be applied to the ignitor to get proper ignition to not wear the ignitor out prematurely. I think the boards may also be "chopping" the power to achive these voltages which would show up better on an analog meter. This may be normal. You may want to also check the quality of the incoming 115 VAC as well as the ground.
    It does not have one of the new boards. I remember now Trane tech support telling me that the unit did have the older type board, and mentioned something about a replacement kit.

  12. #12
    Then the new board may have more ignitor "friendly" circuitry... Funny how nowadays, you seldom see recalls or even "programs" for fixing known issues with things... They know they have problems but they make you pay for the fixes.

  13. #13
    Join Date
    Oct 2008
    Posts
    26
    If the voltage to the ignitor doesnt end up being the problem go to the basics. Remember that furnace short cycling will cause a unit to keep blowing ignitors also. Are you sure that the furnace is not oversized causing it to have too many on and off cycles? Also check things like plugged evap coil and dirty filters or squirrel cages causing the unit to go off on limit. Just trying some alternative solutions. Post what you find out

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event