Results 1 to 13 of 17
Thread: POE OIL FOAMING
    Jan 2011
    Tampa,Fla
    Hmm POE OIL FOAMING
    RECENTLY REPLACED 20 TON DISCUSS COMPRESSOR ON R-22 FREEZER. FLUSHED ENTIRE SYSTEM WITH NITROGEN AND REPLACED TXV BONNET.
    PULLED VACUUM FOR 8 HRS TO 500 MICRONS.
    REPLACED FREON , ADDED ACID NEUTRALIZER TO OIL. REPLACED DISCHARGE OIL SEPERATOR, LIQUID INJECTION DRIER AND BURNOUT CORES IN LIQUID LINE.
    CHARGED SYSTEM WITH 120 LBS R-22 AND AM GETTING A LOT OF FOAM IN CRANKCASE SIGHT GLASS. DON'T KNOW IF LIQUID INJECTION CONTROL IS BAD
    OR WHAT? COLD COMPRESSOR WAS RUNNING WHEN I SHUT IT DOWN, HAD BAD VALVES AND WOULD NOT PUMP DOWN.FREON SMELLED BADDD.
    I AM MAINLY AN AMMONIA TECH, BUT DO SOME FREON.
    Nov 2009
    Richmond, working under tarps
    hot pull down?
    compressor amperage?
    are you positive POE is being used? expensive oil for HCFC refrigerant.
    Jan 2006
    Near Atlanta, GA.
    Welcome to HVAC-Talk.
    This is mainly the new member welcome forum. You'll get more help in the proper forum, in this case the Refrigeration and Ice making forum.
    I'm with k-fridge.
    Repost this in refrigeration and ice-making along with some more system details like pressures and temperatures and we can discuss this in more detail.
    Nov 2010
    Kansas
    Welcome to the site ammoniaman33,
    I can't help with your issue, but wanted to say hello.
    Good luck and take care.
    The statement below is my signature and just my overall feeling towards our industry and does not necessarily pertain to you nor this thread.
    There really isn't a legitimate excuse for not doing the job correctly!
    Jan 2011
    Tampa,Fla
    POE OIL FOAMING REPLY
    THANKS FOR REPLY GUYS, I DID TALK TO A KRAMER ENGINEER AND HE SAID I WAS DOING EVERY THING RIGHT SO FAR, BUT WASEN'T SURE ABOUT THE OIL FOAMING. COMPRESSOR SUPERHEAT IS A LITTLE HIGH BUT NO FLOOD BACK,
    OIL FOAMS UP ON PUMPDOWN AND COMES BACK AFTER DEFROST ENDS.
    THINK MAYBE LIQUID INJECTION MODULE IS BAD OR ACID KILLER IS CAUSING FOAM ? SUCTION PR 12PSIG, DIS PR 200PSIG,EVAP SUPHT ABOUT 10*.
    Dec 2010
    Eaton Rapids, Mi
    YOU COULD CONSIDER TURNING YOUR CAPS LOCK OFF, JUST A THOUGHT!
    Jan 2011
    Tampa,Fla
    seuadr; YOU COULD CONSIDER A MORE PROFESSIONAL MEMBER RESPONSE, JUST A THOUGHT.
    In a machine room
    Quote Originally Posted by ammoniaman33 View Post
    Caps lock on makes it look like you're shouting.
    As k fridge said please post this question in the Refrigeration and Ice Making Forum. Here is a link;http://hvac-talk.com/vbb/forumdispla...aysprune=&f=12
    You will maybe get some more answers.
    Worry is a really gross misuse of one's imagination. -- PHM
    Jan 2011
    Tampa,Fla
    Smile LARGE CAPS.
    sorry bout that, thanks for the info.
    Are you having any problems or did you just notice the foaming oil?
    Foaming isn't abnormal during pumpdown.
    Jan 2011
    Tampa,Fla
    thanks for the reply, this is a replacement comp and oil is foaming while running but pump down causes oil to foam up and leave comp ?
    just started on this website trying to find my way around.
    How high is the oil level?
    Could the crankshaft be hitting the oil during operation?