Results 1 to 11 of 11
    Apr 2005
    Richmond, Virginia
    Thumbs down
    I've just installed 3 Goodman heat pumps, ranging from 1.5 tons to 2.5 tons. I've gotten 2 call backs today (Sunday) and the condensing units are not shutting off when the t-stat is statisfied. They won't even shut off when I turn the t-stat to the "OFF" position. I had to pull the disconnect to get them to shut off.
    My question is has anyone heard if there were a bad batch of condenser boards that got out into the real world? Or am I totally missing something?
    Sean
    Sean Cantrell
    Jul 2002
    Zelienople, Pa
    Probably installation error...
    Jacksonville, FL.
    Originally posted by sean88
    condenser boards
    What are those?
    Toledo, Ohio, United States
    I would venture to speculate that you have a low voltage wiring problem.
    No Heat No Cool You need Action Fast
    not wired correctly.
    Jun 2000
    NC
    Sounds like the O circuit is energized some how.
    o circuit would energize the revrsing valve not energize the contactor.
    Apr 2005
    Richmond, Virginia
    I forgot to say the units were working properly during start up, they cycled on and off, went from cooling to heat, etc without a hitch. They were installed approx. 6 months ago.
    Sean Cantrell
    Are these both on the same job site?
    Multimeters are your friend.
    Did you check to see if the outdoor units had 24v to Y and or O when the thermostat off?
    Did you perform any other diagnostic work beyond turning off the thermostats?
    The units running after you turn the thermostats isn't enough diagnostic work, there are many things that could be causing your problem.
    cocoa fl
    sounds like you have the unit hard wired meaning it has been wired to run all the time. if you know even a little about troubleshooting you can find the problem.