Thread: Why oversize the indoor coil?

  1. #41
    Join Date
    Feb 2004
    Location
    Pacific NW
    Posts
    879
    Post Likes
    If you plot out the T-s and pressure on a Mollier diagram for a given compressor flow rate, you will see that a LARGER evap and condensor will almost always increase COP. Only exception is if the pressure drop thru longer tubing lengths compormises efficiency.

    My own custom system has a 7-1/2T condensor on a 4T scroll compressor and custom tube in tube evaporator (GSHP) and has a COP of 5.6. Ends up that the bottom 2 coils of the condensor fuchtion as a receiver.

  2. #42
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    Maybe, but he has a HP and and that may not be true, I have "always" heard on a HP system, the coil and condenser should match tonnage wise.

    These Tax credit systems are sometimes really strange. We just installed a Ruud system, 3ton that required the 100,000 btu furnace with the Ruud coil, and a 75,000 furnace with the Aspen coil, go figure. In Ohio this might be a good thing, but in Texas, I am sure the furnace will short cycle.
    It is not uncommon to have a larger coil for a heat pump, the reason being it gives more surface area to transfer heat and on the cooloing side it gives more surface area for better dehumidification.

    I installed a Goodman unit for a friend of mine, he it was a 3.5 ton system, the same air handler was used on 3.5 to 5 ton units, the only difference was the expansion valve, it was a variable speed unit.

    He bought it from a distributor that would sell to anyone, it was pretty cheap that is why he bought a Goodman, other than the goofy beer coozy for the TXV it wasn't a bad unit.

    I am an American Standard dealer and their air handlers match up to varying sized condensing units and the TXV is the only difference.

  3. #43
    Join Date
    Jan 2011
    Location
    New England
    Posts
    4
    Post Likes

    That would make for a whole lot of static pressure...

    Mr Bill, What are some pros and cons when you have high static pressure, that you've seen over the years you've worked in the field?

  4. #44
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Delta-T View Post
    Mr Bill, What are some pros and cons when you have high static pressure, that you've seen over the years you've worked in the field?

    Increased static, could be a problem, if the indoor fan is not capable of handling the increased static pressure, usually results in decreased airflow across the indoor coil, and could lead to excessive wind noise from the registers. Reduction of the airflow usually, in turn, leads to lower temperature of the indoor coil, because the amount of air moving across it, and is no longer able to maintain the proper temperature. Now this is just what I have personally witnessed, there may be others with differing opinions.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  5. #45
    Join Date
    Dec 2006
    Location
    Just South of Indianapolis
    Posts
    19
    Post Likes
    Go to the ari.org site and see what coil matches what outside unit and what the rated cfm to achieve proper efficiency is. Coils seem to be numbered to match the lowest efficiency outside unit. Increase outside coil for efficiency and the refrigerant needs larger inside.

  6. #46
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    I guess I am not being clear about my "only grief" with these new high seer systems.

    beenthere: the furnace has a 5-ton drive, to me that's saying 2000 cfm's, it has the X13 ECM motor. The X13 has the electrical efficiency of the ECM, but has fixed speeds like a PSC.

    Ok that said here's been my point all along, how many service companies "after" the installation set the motor speeds, via "dip switches or whatever" for best sensible and latent removal?

    And if they do try and set the speeds in good faith, has this done anything to the beginning efficiency?
    Ok example, we have a service co. that has now set the speeds to perform the best, and in my opinion, there still guessing "somewhat" so now we have a 5-ton drive 2000 cfm furnace running at 1580 cfm's. Everything is cool and there gone, so why did I just buy a 5-ton drive 2000 cfm furnace, when a 4-ton drive 1600 cfm would have been fine, is anyone following me?

    Someone said is the motor variable, well even if it was, in hot and humid Houston Texas, in the middle of the summer, when it's 100* out with 95% humidity, is it going to be running in high cfm or low? in high were kicking some sensible but no latent, in low were kicking some latent but less sensible, to me, if your losing anyone of the two, your loosing capacity. I am not condemning the new higher seer stuff, I just think the Government view of the tax credit systems are a little off.
    If its a VS. You would set the blower to start with a slow ramp up, so that in the beginning of the cooling cycle it removes more humidity.. And then increases speed to remove more sensible.

    Areas with both high sensible and latent loads. Benefit from a thermostat that can slow down the blower if need be to remove more moisture, and then allow it to speed back up o handle the sensible load.

    The 5 ton drives X 13 motor running at a lower RPM to move 1600 CFM will use less electric then a 4 ton drives X 13 at a higher RPM to move 1600 CFM.

Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •