PVC FOR OIL FILL LINE
Results 1 to 6 of 6
  1. #1
    CAN PVC PIPE BE USED FOR THE FILL AND VENT PIPING ON A OIL FURNACE SETUP?

  2. #2
    I have always used black pipe only, I know it is code where I am to use black pipe only for oil tank fills.

  3. #3
    Join Date
    Feb 2003
    Location
    S.W. PA
    Posts
    3,298
    no!!! use black iron

  4. #4

  5. #5
    Join Date
    Dec 2000
    Location
    Central PA
    Posts
    244
    For many years in this area PVC was used for vent piping and to my knowledge nothing bad has ever come from that. That being said, what you will find in most cases is that codes REQUIRE black iron piping and if anything would go wrong with the PVC piping, chances are your insurance company would not cover damages due to the code being violated.
    SRJ

  6. #6
    Join Date
    Jan 2005
    Posts
    7

    fill and vent piping

    Per NFPA 31 8.2 Acceptable Piping MAterials: "Tank fill and vent piping shall be wrought-iron,steel, or sched 40 Brass pipe" Remember, plastic pipe and glue are oil based so you can end up dissolving them.