    Does this sound like a faulty flame sensor?

    Howdy folks,

    I have a three year old Goodman two-stage LP furnace (GMH95) that's giving me a problem. When I call my heating and cooling guy I want to sound like I know what I'm talking about.

    Here's the problem:
    About 70% of the time when the furnace tries to ignite, the electronic igniter glows red for about 7 seconds but the burners don't ignite so the igniter turns off. It tries again after a few seconds and if there is no ignition, it gives up. If I turn the thermostat off and back on, it will go through the process again and will eventually ignite, sometimes after one or two more resets.

    As a result, I wake up to and come home to a cold house but can get the furnace to kick on after a few tries.

    This sounds like a likely bad flame sensor, right? This is all under warranty but I'd like to hear your thoughts before I talk to my heating and cooling guy so I don't sound clueless.

    Thanks,
    Grif

  2. #2
    Join Date
    Jun 2008
    Location
    Cincinnati, Ohio
    Posts
    2,176
    Maybe.......

    Do the burners actually ignite and go off after a few seconds, or do they never ignite?

  3. #3
    Join Date
    Dec 2010
    Location
    Chillicothe, Ohio
    Posts
    19
    If the burners do not ignite, then it is NOT a flame sense issue.

  4. #4
    Join Date
    Jan 2011
    Posts
    6
    Quote Originally Posted by phbsales View Post
    Maybe.......

    Do the burners actually ignite and go off after a few seconds, or do they never ignite?
    Thanks for the quick reply, phbsales. When the burners light, they stay on. The problem is getting them lit. I can look through the peep hole in the cover and I know when I see red, it's the electronic igniter glowing. When I see blue, the burners have ignited. I never see blue for just a couple seconds; when it ignites, it stays on.

  5. #5
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    2,916
    Maintenance should be done on that furnace every year, when was the last time?

  6. #6
    Join Date
    Sep 2006
    Location
    Montana
    Posts
    983
    Like what was stated earlier, if the burners do not light, it's not a bad flame sensor. If the ignitor is now glowing through it's entire warm-up period, there may be a pressure switch opening or the circuit board is faulty. It could also be several other things, but it's hard to say without seeing it. I wouldn't be concerned about what to tell the tech, it's his job to diagnos it. Just call and tell him that the furnace is intermittently working. When he arrives to look at it, describe to him what you've observed and let him fix it.

  7. #7
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    2,013
    Quote Originally Posted by Grif View Post
    Howdy folks,

    I have a three year old Goodman two-stage LP furnace (GMH95) that's giving me a problem. When I call my heating and cooling guy I want to sound like I know what I'm talking about.

    Here's the problem:
    About 70% of the time when the furnace tries to ignite, the electronic igniter glows red for about 7 seconds but the burners don't ignite so the igniter turns off. It tries again after a few seconds and if there is no ignition, it gives up. If I turn the thermostat off and back on, it will go through the process again and will eventually ignite, sometimes after one or two more resets.

    As a result, I wake up to and come home to a cold house but can get the furnace to kick on after a few tries.

    Thanks,
    Grif
    By calling and telling the service company exactly what you wrote above....... you're already sounding more informed than possibly 90% of the customers that call more than likely.

    Tell them just what you wrote and allow their technician to diagnose what is going on. Sometimes giving too much information, especially to the technician, can in some cases sway them to jump on what you think it is.

    They're there for two things, fix the problem and leave with you being a happy customer. Sometimes making the customer happy gets in the way of digging deep enough to find the real problem.

    Trust them to know what they're doing and to take the information you've supplied here and make things work perfectly again.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  8. #8
    Join Date
    Sep 2010
    Location
    Wa.
    Posts
    119
    I would just say everything that you all just said. Have a tech out , shouldn't be too bad to troubleshoot.

  9. #9
    Join Date
    Jan 2011
    Posts
    6
    Good advice, everybody. I think I know enough to sound knowledgeable when I talk to the tech.

    Regarding the Goodman warranty, do you folks have positive experiences with the company? I ask because I see this on the website:

    "To receive warranty online registration must be completed within 60 days of installation."

    When it was installed three years ago, I never received any registration information from my tech and did not know I had to register. On the Warranty and Registration Lookup section of the Goodman site, my name is not found in their database. I can look up by serial number but am not sure where this is located on my furnace. I'm worried the warranty will not be honored because I did not complete any registration when the furnace was installed.

  10. #10
    Join Date
    Jan 2011
    Posts
    64
    I am a Goodman dealer. I sell many of them. They have, until recently, not had a very good name because of the failure rates of the furnaces even though they outsell every other manufacturer in the country. THis was mainly because anyone could buy and install Goodman, you wouldn't believe some of the installs I've seen on service calls - I'm surprised they stayed running for a week after the install.

    If your furnace is still under its warranty period, and you call someone who is a goodman dealer/ installer, than it won't matter if you sent in the paperwork. That can all be looked up by the model and more importantly the serial. Your parts will be covered, but probably not the labor.

    It's not the flame sensor if it will only ignite intermittently.

  11. #11
    Join Date
    Jan 2011
    Posts
    6
    Quote Originally Posted by slowguy View Post
    If your furnace is still under its warranty period, and you call someone who is a goodman dealer/ installer, than it won't matter if you sent in the paperwork.
    Thanks for this information, slowguy. My heating contractor is a Goodman dealer so it sounds like there won't be any issues with getting the parts covered.

  12. #12
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,104
    If you want to sound intelligent when talking to your tech. just tell him you saw the HSI glow, but the burner never ignited.

    If you try telling him more then that. You won't sound intelligent.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #13
    Join Date
    Feb 2010
    Location
    Cal
    Posts
    1,596
    If you try telling him more then that. You won't sound intelligent.

    You have me giggling and shaking my head

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event