I know the gas supply is an issue that has occured prior on other units around this facility, that is still in the process of getting resolved. This unit would not fire at times when I still had 8-9" inlet press. and about 8" between honeywell and maxitrol valve. Is there a setting on downsteam side of the modulating valve (manifold) I should be looking for? Was informed to not even pay attention to this. Was this legitament advice?
-
01-20-2011, 11:42 PM #15
I don't pay any attention to manifold pressure if airflow is correct and unit will make rated rise at high fire.
If the honeywell valve has a fluid power actuator; I have seen a few actuators intermittently run slower than rated when cold and of course if it loses fluid, which could cause a flameout.
I also wonder what the flame current is pilot only and also main flame high and main flame low. Should be well above minimum when things are right.
If gas pressure is remotely a problem and hard to catch, I've installed temporary manual reset low gas safety switches to prove or disprove the possibility. Not wired, just connected to inlet gas.
And then there's the flame sense lead and sensor, if either starts to fail, fine hairline cracking, it can work ok when dry but not when wet. Check the flame sense lead and sensor on high megohms. I use a 60 megohm meter for this, should show infinity if good.
-
01-21-2011, 07:07 AM #16
Professional Member
- Join Date
- Jan 2008
- Location
- Jackson, MI
- Posts
- 111
What condition is the ground wire going to the burner. Corrosion will cause sensing problems
-
01-21-2011, 08:38 AM #17
If this is a direct fired make up air unit the manifold pressure operates in a negative and typically needs much higher inlet pressure to account for required btu output. manifold pressure on these type of burners is super critical. especially on low fire which is what will prove your flame snensor.
NOTE: On these type of burners you can still have your inlet pressure but not the volume of gas output.
-
01-21-2011, 04:23 PM #18
-
01-21-2011, 04:28 PM #19
I wouldn't worry about it at this point. A couple questions;
Are you able to see the pilot being lit?
What is you pilot regulator pressure?
Is this a interrupted or intermittent pilot?
Do you know what manufacture of burner is it? I thought those ran Maxon burners.
If it is a Maxon burner......was the ignitor ever replaced?
If it was.....make sure the right ignitor is in there. They come in a couple of different lengths, depending on the end plate.
-
01-21-2011, 05:07 PM #20
Regular Guest
- Join Date
- Aug 2004
- Location
- Des Moines, IA
- Posts
- 76
looking forward to ascj's questions, I had issues with dirty pilot burner at ignition source and igniter points
-
01-21-2011, 06:03 PM #21
Regular Guest
- Join Date
- Oct 2002
- Location
- North central Massachusetts
- Posts
- 793
I'm curious about the fact there is a vfd involved if this is a direct fired make up air unit. I've serviced and started up many Greenheck, Reznor and Cambridge Air units and never had a vfd involved. On my understanding of their desired design and application I would think a vfd would affect the operation. I'm not saying I'm right, just never seen it since burner velocity and exchange of air are critical on those. I would like to hear from others who have.
-
01-21-2011, 06:10 PM #22
-
01-21-2011, 06:28 PM #23
Regular Guest
- Join Date
- Oct 2002
- Location
- North central Massachusetts
- Posts
- 793
Ah Ok . Thanks ascj. for that. Maybe I'll get to see one set up like that since people do see a lot of weird stuff in this trade.
-
01-21-2011, 06:35 PM #24
Professional Member
- Join Date
- Jan 2011
- Location
- minnesota
- Posts
- 22
I am able to see the flame fairly good when lit, or burning. Flame looks fine. There is no actual separate pilot for ignition. It lights on low,or min. flame. Once burner lights, and flame is proven amplifire and modulating valve takes over. I did adjust min. fire rate so had suggested reading (1-2 uf) on flame sensor. Do not know if ignitor has been replaced or not, but did clean and set gap to specs. I did try swaping out w/dif ignitor and still had same issue.
-
01-21-2011, 09:16 PM #25
-
01-21-2011, 09:29 PM #26
My gut feel is your on the right track with adjusting up low fire gas pressure, it should in turn increase your flame sensor signal strength, but the big question " is it constantly maintaining the proper gas pressure" or sporadically dropping when the building is under a high gas demand condition. I suspect with a known building gas pressure issue that I would strongly urge that be resolved first. ( It is possible that the unit gas pressure regulator may be under sized or sticking. If its outdoors Ive even had them freeze up. All they are is a diaphram with spring) Then see if your still having flame failure problems. I know it sounds strange but trust me on this one.


Reply With Quote