    EFFICIENCY
    In the English l‑P system, chiller efficiency is measured
    in kW / ton:
    kW / ton = kW input
    tons refrigerant effect
    In the Sl Metric system, chiller efficiency is measured
    in Coefficient of Performance (COP).
    COP = kW refrigeration effect
    kW input
    kW / ton and COP are related as follows:
    kW/ton = 3.516
    COP
    COP = 3.516
    kW/ton
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  2. #15
    Join Date
    Feb 2006
    Posts
    226
    Post Likes
    EFFICIENCY
    In the English l‑P system, chiller efficiency is measured
    in kW / ton:
    kW / ton = kW input
    tons refrigerant effect
    In the Sl Metric system, chiller efficiency is measured
    in Coefficient of Performance (COP).
    COP = kW refrigeration effect
    kW input
    kW / ton and COP are related as follows:
    kW/ton = 3.516
    COP
    COP = 3.516
    kW/ton
    I think kw/ton and COP are two ways of describing the same thing only inverse of each other. kw/ton is" motor kw divided by tonnes of refrigeration."
    Where as COP is" kw refrigeration divided by motor kw."
    kw Refrigeration is tonnes x 12/3.41

    Jay, most 19XR's or YK with VSD will show power factors of 0.95-0.98.
    A power factor of 1.0 or greater will damage a motor windings. It wont matter much to the calculations.

  3. #16
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    Power Factor can "Never" be greater than 1.
    A power factor of 1 indicates a purely resistive load.
    The power factor we always see would properly be stated as .95lag-.98lag ect.
    Going beyond a unity power factor of 1 results in the forbidden realm of "Leading power factor",(Capacitive load) again always less than 1, and would be stated as .95lead-.98 lead.(example)
    Please...No more references to "Greater than 1 power factor"...It just ain't there...
    Ain't "None" of us as smart as "All" of us..

  4. #17
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    GREAT!!!!!!!!!!!!!!!!!!!

    Great equipment room reading!!!!!!!!!


    Quote Originally Posted by jayguy View Post
    true knowledge exists in knowing that you know nothing.

  5. #18
    Join Date
    Jul 2012
    Posts
    25
    Post Likes
    Are the power factors of these devices close enough to 1.0 that a capacitor is not needed on the secondary of the contactor? I would expect to find a power factor improvement capacitor on every device but I haven't seen a single one. Also, since it would only be active when the device was running and would be on the 240 VAC line with the rest of the branch circuits, I don't see any detriment to installing one at each chiller.

    Thoughts?

  6. #19
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,803
    Post Likes
    Quote Originally Posted by jayguy View Post
    Damn Jay, you got me sidetracked and I forgot what this thread is about!!!

  7. #20
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,937
    Post Likes
    Quote Originally Posted by R123 View Post
    Damn Jay, you got me sidetracked and I forgot what this thread is about!!!
    i forgot i did that too!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  8. #21
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,937
    Post Likes
    Quote Originally Posted by Priya1956 View Post
    Are the power factors of these devices close enough to 1.0 that a capacitor is not needed on the secondary of the contactor?...
    if you are talking about a vfd/vsd type of system, then you generally don't need or want a Power Factor Correction Capacitor between the line side of the drive and the utility. you definitely don't want any PFCC's between the drive and the motor.


    Quote Originally Posted by Priya1956 View Post
    ...I would expect to find a power factor improvement capacitor on every device but I haven't seen a single one....
    PFCC's have a lot of great things going for them, however, they are generally misunderstood and/or misapplied. PFCC's can cause a harmonic resonance in the power wiring of the system if they are not engineered properly...this generally doesn't happen, but it can.


    Quote Originally Posted by Priya1956 View Post
    ...Also, since it would only be active when the device was running and would be on the 240 VAC line with the rest of the branch circuits, I don't see any detriment to installing one at each chiller....
    i have seen many instances where they were sized for the chiller, installed AT the chiller but on the wrong side of the contactors (in a non-vfd chiller). this allowed for Power Factor Correction for the whole plant when the chiller wasn't running. every once in a while....BOOOOM.... and then every maintenance person running around like crazy. there are generally 2 different ways to install PFCC's and a 3rd hybrid which is what i like.

    1. install a big power factor bank at the utility entrance...the good: corrects for the whole building to 95% or so...the bad: only helps the utility, the building doesn't get any benefit except for a lower utility bill (which is nice, but there are other benefits that are missing)

    2. install a PFCC at every end device...the good: allows for better voltage regulation throughout the facility and a lower utility bill....the bad: high install cost and higher maintenance costs.

    3. install a PFCC at all of the non-vfd major loads (chillers, pumps, fans) and install a smaller PFCC bank at the enterance...the good: better voltage regulation throughout the facility, lower utility bills, lower overall costs, the PFCC bank can still be used to perform a final correction to 95% or better...the bad: still has a high cost per device but not as bad as Option #2.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  9. #22
    Join Date
    Jul 2012
    Posts
    25
    Post Likes
    The hybrid approach seems best especially as it improves power factor only on demand without the risk of overcompensation. Sounds like the big hurdle is quantifying the benefits beyond a reduction on the utility bill. How to put a $ value to better voltage regulation?

    Assuming that the capital cost of the PFCC is recovered only from a utility bill reduction, what is the typical payoff period for a device installed PFCC? Perhaps it is too long for owners to spend the capital up front??

  10. #23
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,937
    Post Likes
    the benefits are difficult to quantify. like you said, you are helping them with 'savings' which is a negative cost and very difficult to prove. you are usually going to find the only customers who want this are large users, people who understand the benefits and those that are already having problems.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.