Results 1 to 13 of 23
    US
    kw per ton w/vsd
    Ok formula guys, Question, to get kw per ton on a chiller with vsd. Tonnage no problem gpmXdelta p / 24 now for kw do i just use supply voltage and amp clamp on supply line or should i use the reduced volatge that the motor is running at and amp clamp on motor lead. Then is it kw/ton or ton/kw. I think I am confusing myself.
    LOL!!!!!!!!
    it is kw per ton!
    1 being bad
    .5 being good
    true knowledge exists in knowing that you know nothing.
    funny!
    I always figured since it is 746 watts per horse power and usually 1 or 1.1 hp per ton .746 kw per ton would be the best you could do!
    then volts x amps x 1.73 div by 1000
    you need to look at the line side of the drive and NOT the load side
    there will be an energy penalty when using the drive as it consumes some power no matter how much the chiller is using and you need to include that energy in your calculations
    Jay,
    got any more good reading material links for me????????
    Dec 2008
    Dixiana, AL
    Quote Originally Posted by 9675 View Post
    GPM x delta T /24
    aaaaaaaaaaaaaaaah!
    T,P? same thing!!!!!!!!!!!
    Quote Originally Posted by klove View Post
    GPM x delta T /24
    kind of neet kw per ton chart for turbocor
    http://www.turbocor.com/literature/p.../aircooled.pdf
    Quote Originally Posted by supertek65 View Post
    don't forget to compensate for power factor...it should be close to 1.0...but it may not be!
    US
    opps yeah delta t, ok thanks for input, how do ad for power factor of 1.0
    Jay,
    http://www.good-reading-material.com
    ...how do ad for power factor of 1.0
    you have to have a power factor meter to measure it.
    if you are just figuring things out for yourself, then just use 1.0
    if you are commissioning a unit or anything like that, you will need to measure more accurately.