Results 1 to 13 of 14
-
01-19-2011, 07:12 PM #1
Professional Member
- Join Date
- Oct 2009
- Location
- Mukwonago, WI
- Posts
- 204
automatically start a kitchen hood system
What do you guys use? Captive Aire supplied a in-duct switch that closes at 85°. It's a little pricey, i was looking for a less expensive alternative.
Any suggestions?
-
01-19-2011, 08:19 PM #2
Professional Member
- Join Date
- Jan 2008
- Location
- Jackson, MI
- Posts
- 111
Not s.ure exactly what you're referring to but usually I see just a simple on/off switch. You might have a control that turns the system on and off based on temperatures from cooking equipment that only runs when equipment is on. That would save utility money that would more than pay for the expensive switch
-
01-20-2011, 10:14 AM #3
Professional Member
- Join Date
- Jan 2011
- Location
- Russellville, Alabama
- Posts
- 26
Have you thought about using a line voltage thermostat - like Johnson Controls? Don't know if it would be cheaper than your switch, but will definitely work.
-
01-20-2011, 11:05 AM #4
Regular Guest
- Join Date
- Apr 2010
- Location
- N. IL
- Posts
- 8
look into Melink Intelli-Hood systems or something along those lines, they use temp sensor(s) and a set of optics and a vfd to control it. easy to use and install. offers great money savings too
-
01-20-2011, 12:08 PM #5
Professional Member
- Join Date
- Dec 2004
- Location
- Albuquerque, NM
- Posts
- 101
The hoods should be turned on when the equipment is started for the day. What exactly are you trying to accomplish?
Mark
-
01-21-2011, 10:27 AM #6
Professional Member
- Join Date
- Oct 2009
- Location
- Mukwonago, WI
- Posts
- 204
IMC 507.2.1.1 states Type I hood systems shall be designed and installed to automatically activate the exhaust fan whenever cooking operations occur. The activation of the exhaust fan shall occur through an interlock with the cooking appliances, by means of heat sensors or by means on other approved methods.
Currently we get a vulcan cal-stat from Captive Aire that is installed in the grease duct and turns the system on when it reaches 85°. This item is a little pricey from Captive Aire and i'm looking for a more cost effective alternative. I'm just curious what other people use.
-
01-21-2011, 04:38 PM #7
Professional Member
- Join Date
- Dec 2004
- Location
- Albuquerque, NM
- Posts
- 101
I would stick with what the manufacturer sells. That hood has a UL listing. I don't think NM goes by that code.
Mark
-
01-21-2011, 04:43 PM #8
Regular Guest
- Join Date
- Aug 2004
- Location
- Des Moines, IA
- Posts
- 76
How bout heavy smoke and less than 85
-
02-09-2011, 10:13 PM #9
Professional Member*
- Join Date
- Jun 2004
- Location
- St Paul, minnesota
- Posts
- 766
-
01-18-2012, 11:55 PM #10
-
01-19-2012, 09:49 PM #11
Professional Member*
- Join Date
- Jun 2004
- Location
- St Paul, minnesota
- Posts
- 766
if you have the standard captive UL listed heat sensor system with PLC'S just reset the control to a higher temperature so that hood MUA EXH only come on when main burners are on. ( personally I set mine at 115 degrees)
-
02-23-2012, 12:25 AM #12
Regular Guest
- Join Date
- Sep 2011
- Location
- Maryland
- Posts
- 27
-
02-23-2012, 11:56 PM #13


Reply With Quote