    Outside unit 3 ton Trane XL19i, Inside unit 040 Trane Variable Speed air handler. Stat is 302C 2-stage. No humidistat. in cooling, air handler seems to run at 100% regardless of Y1 called for vs. both Y2/Y1. Shouldn't it ramp up/down 50-80-100-80-50 right?
    DIP 5/6 "On".
    LVTB has W1-W2 Jumper and R-BK jumper. Is R-BK jumper correct for Comfort-R? Another Jumper (R-O or YLO-O needed?)

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    There is a sticker on the blower housing telling you where the dip switches need to be set depending on the size, desired cfm per ton, blower timings, etc.
    The blower timing dip switches are #5 and 6. I believe they both need to be on for Comfort-R.
    If your system is a heat pump, no jumper is needed between O and Ylo. If it is straight AC with electric heat or a gas furnace, you need to put a jumper between O and Ylo for Comfort-R to work correctly.
    The jumper from R to BK is factory installed.

    If you want Comfort-R to work in the heating mode, go ahead and put the jumper in between O and Ylo, but do not connect O from the thermostat or the outdoor unit to the O terminal in the indoor unit. Wire O from the thermostat directly to O to the outdoor unit.

  3. #3
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,849
    Post Likes
    In addition to mark's comments, the 302C is factory configured for 1 heat / 1 cool. Has this setting been adjusted per the installation manual?

  4. #4
    Join Date
    Mar 2005
    Posts
    2
    Post Likes
    Thread Starter
    I think 302C is right, Y1 and Y2 activate separately as indicated by different LEDs on the DIP board.

  5. #5
    Join Date
    May 2004
    Posts
    61
    Post Likes
    Trane 19i doesn't energize y1 and y2 at the same time. Ylo enrgizes then after 10 minutes it drops out for around 45 seconds and then the Yhi is energized. Also make sure you've got your Ylo and Yhi wired correctly because it sounds like you going straight into Yhi.

  6. #6
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,849
    Post Likes
    The thermostat will keep Y1 and Y2 energized. So, both lights will be energized on the control board. As a matter of fact, the ODU won't run without both Y1 and Y2 present at the ODU. You are confusing compressor operation with low voltage signals.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.