    i have a chiller for an mri machine that went down , i can not get flow down in the room , i think the bundle is frozen? i checked the pump and it has the correct amps , shut of the discharge and it dead heads fine, but doesnt dead head like its frozen over , i tried putting water back into the system. but nothing down in the room. i did check freeze point and the glycol is gone , im going with a heater and tarp tomorrow , w

  2. #2
    Join Date
    Aug 2010
    Location
    Memphis
    Posts
    343
    Doesn't the machine have a low temp or pressure cutoff to keep it from freezing or does it run below freezing. It ought to have a flow swith as well.

  3. #3
    Join Date
    Jan 2011
    Location
    Wentzville, MO
    Posts
    6
    it goes into city water flow when it shows a no flow condition from the chiller, it does have low pressure cut out and a stat for water temp. that all works its the water flow that i cant figure out completely. its some sort of water flow issue

  4. #4
    Join Date
    Nov 2010
    Location
    Andover Kansas
    Posts
    2,115
    Welcome to the site Dan,

    Rules won't let us give too much technical help out here in the open forums, but get your posts up to 15 and apply for pro membership, then you can join us in the pro section.

    Enjoy the forums and take care.
    .


    The statement below is my signature and just my overall feeling towards our industry and does not necessarily pertain to you nor this thread.


    There really isn't a legitimate excuse for not doing the job correctly!

  5. #5
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,529

  6. #6
    Join Date
    Nov 2010
    Location
    Andover Kansas
    Posts
    2,115
    Quote Originally Posted by k_fridge View Post
    Moving to chiller forum where you'll get more responses
    I was hoping one of you might come along and do that.
    .


    The statement below is my signature and just my overall feeling towards our industry and does not necessarily pertain to you nor this thread.


    There really isn't a legitimate excuse for not doing the job correctly!

  7. #7
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    I have a MRI that has a manual bypass valve for water balancing. We have to open it enough to make the flow switch, open it too much and we lose flow to the MRI.

  8. #8
    Join Date
    Jan 2011
    Location
    Wentzville, MO
    Posts
    6
    the pump had went down and the lines dumped the water glycol mix , it was frozen from the check valves on , and we found that the unit dump valve was now bad , it was a good experience, now we are finishing it on a sat afternoon when we can shut the entire system down

  9. #9
    Join Date
    Aug 2008
    Location
    Philadelphia
    Posts
    84
    Those MRI machines are great for OT. Enjoy your Saturday!
    Do not weep, do not wax indignant. Understand.
    -Spinoza

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event