Page 3 of 4 FirstFirst 1234 LastLast
Results 27 to 39 of 48
  1. #27
    leland nc
    rhblake57
    you misunderstand me a little on this
    the ubend in the candensate pipe should not be fill with water in december
    i was talking about the flex runs to the registers in the cieling. if cold air is aloud to draft throught them in cold weather they can condensate and collect water over the winter
    with hot air rising up throught the return and cold air falling from the registers into the house can cause this to happen in the supply runs to the registers
    the condensate line from the unit should not have water added to it because it will freze and crack
  2. #28
    To Icimpala65 3-27-05
    I'm saddened you feel so negatively about my concerns.
    Secondly, I'm not "looking for something to use against my contractor"
    I am hoping to understand enough about my system to help my contractor solve the problem he either can't or won't.
    If he won't then I will have enough knowledge to help another contractor solve my problem.
    Another kind expert on this site differs with you, and was kind enough to pass on a link to a Carrier site, that displays a chart showing that the optimum humidity percentage is between 40 ad 60 percent.
    While not everyone will be happy at 40 to 45 percent, I was.
    I believe that Carrier/Bryant publishes that info because it is true.
    My system last summer never got below 50 percent and was often 55 percent.
    I wanted what Carrier/Bryant promises.
    Hopefully, when I have enough info from you and other caring experts in this field of expertise, I can pass this info on And my contractor will do the neccessary work, if there is any left to be done.
    He then will have that knowledge if the same problem arises with his future customers.
    I'm now happily retired. I learned in my 45 years as a very successful salesman, that if a customer believes he has a problem with my product, then he has a problem that needs to be resolved to his satisfaction. Not my satisfaction!! In 45 years I never had one unresolved customer concern. Period!
    Anybody can sell a product. The man or company who doesn't sell satisfaction with that product will be out of business in a few years.
    Of course, I'm sure you already know this, and that you do everything to resolve your customer's problems.
    Thanks again for your help rhblake57@comcast.net
    Originally posted by lcimpala65
    Have we not all encountered this in the past? The humidity in the house is fine. The fact that the humidity OUTSIDE the home is 70% or higher is not relevant, the five gallon bucket story isn't relevant, what is relevant is the actual humidity level in the home,period. The equipment is maintaining proper humidity levels IN the home, the levels are industry standard, the unit is cooling the home satisfactorily; what else do we expect the equipment to do?. This gent wants something fixed that isn't broke. It's the same old story, it doesn't work as good as the junk he had replaced, and he bases this on what? how many drops of condensate he sees flow out of the air handler. Give me a break!! Older folks never can adjust to the newer technology used in modern heating and air equipment, his contractor and Bryant has given up on him because there is NO problem. You can't fix what isn't broke. Now I know mister home owner you will be mad about this post, but trust me NO ONE on this site is going to fix this for you, or give you a magic bullet piece of info that you can use against your contractor. The fact is you don't have a problem.
  3. #29
    To Chillbilly 3-27-05
    I guess this is the old shoulda, coulda, woulda. I'm not sure the workers for this contrator were very qualified.
    If I had met theworkers when I met him, I don't believe that I would have hired him. They made a lot of other errors such as:
    1 A plasic plug removed from the coil was left in the condensate pan and blocked the drain pipe and flowed over into the secondary pan under the air handler. Of course the feed ductwork to all the rooms was soaked, but they would not replace them as they insisted that they would dry out when I ran the system awhile.
    2 After that visit they had to return again since the air handler coil runoff pan was sloped completly to the back of the unit so water was pooling at the back of the air handler.
    3 They pushed a light fixture in my hall ceiling through the attic floor and tied it back up with plastic ties. Of couse they never told me, and I only noticed a month later when plaster started to fall off the ceiling in my hallway that leads to the bedrooms.
    4 At point of sale, the contractor assured my wife and me that I had a 3 ton air handler despite my having a 2.5 ton tag on the condenser outdoors. So he sold and installed a 2.5 condenser and a 3 ton air handler. I did not know how to read the air handler tag. Fortunately the Bryant dealer/distributer swapped it at no charge for a 2.5 ton air handler. I had to pay the contractor an additional $300 cash for the labor to remove and swap the unit.
    The contractor refused to downsize the plenums into and out of the air handler which were now much too big for the smaller 2.5 ton air handler. So they are attached, but hang over the entry and exit to the air handler.
    Shoulda, coulda, woulda would be a good title for this thread.
    Thank you for your thoughts rhblake57@comcast.net
    Originally posted by chillbilly
    Superheat/subcooling should have been measured during startup as well as airflow,air leakage, amp draws, delta T, etc, etc.
    I have a hard time understanding how those basic things were not checked if indeed, they weren't.
    If your indoor humidity level is within the desired range, and the s/a vs r/a temp difference is within spec, the system may be doing exactly what is required.
  4. #30
    To tiknocker 3-27-05
    Are you saying that despite being insulated the ductwork can build condensate? Should I always close off the grills and put plastic around the return filter in the hallway as I did this past winter?
    Thanks again rhblake57@comcast.net
    Originally posted by tinknocker service tech
    rhblake57
  5. #31
    West TN
    Now that we have a clearer understanding of the quality of work that has been performed, then I highly recommend getting a 'qualified' contractor to come and diagnose the system.
    Extend to others the grace that God has given you.
  6. #32
    [QUOTE]Originally posted by rhblake57
    [B]To Chillbilly 3-27-05
    rhblake57;
    I see that there are some serious issues with sloppiness during installation.
    It is OK to upsize the airhandler in various instances up to 1/2 ton...no problem.
    So, if you have a 2 ton condensing unit, it would not necessarily be an error on the contractors part to have upsized the indoor unit 1/2 ton.
    That noted, condensate plugs and incorrectly sized trunk duct WILL cause some major problems.
    There is no reason I can think of why that system will not dehumidify to the lower end of the comfort envelope (45%) easily if (and it's a big if) the design and installation parameters are satisfied.
    Also, I somewhat agree with your assesment of the customer being king but I do understand that many customers are not adequately informed as to the requirements that a system will meet.
    I know that there cannot be 100% satisfaction in this business. It simply cannot be attained, regardless of how hard we try (and most of the people here do try very hard)
    I understand ICIMPALA'S frustration but I would continue to try and solve any issues with dogged persistance for the customer. You have every right to complain if you are not satisfied.
  7. #33
    Apr 2003
    Cullman Alabama,
    What did you sell?
  8. #34
    To lcimpala65 3-28-05
    You have an intriguing web name. I'll bet that there is an interesting story behind it.
    I sold waterless greaseless cookware directly to consumers in their home 1957 to 2003.
    Best wishes for success to you
    What did you sell?
  9. #35
    When it warms up,check the temperature drop,in and out of the air handler,and post it on this site.
    My guess is the TXV was overheated and damaged when the system was installed.It is in the air handler,you could look to see if the bulb is attached to the suction line.
  10. #36
    West TN
    Thanks for the reminder Dash.
    Though it brings back bad memories hehe.
    Had a Carrier air handler that had the same prob.... TXV bulb over heated... (On top of that, the liquid line was undersized. Talk about a wierd one to diagnose.
    Bad thing about it.... it was our installers that did it arghhhh. They grabbed 5/16 instead of 3/8. And one of the peons made the welds.
    TXV bulb didn't stand a chance being that its only a couple inches away from the weld. Add the fact that they didnt' use any heat block on it.
    Least I found out the hard way that Puron DON'T like the wrong line sizes. It makes a HUGE difference.
    Wished I woulda wrote down what kinda pressures and temps I had when it was all screwed up.
    All I remember was the pressures at the unit were going up and down. It was acting like it was flooding for about 30 seconds then starving for 30 seconds. Along with way too much liquid to not enough liquid. It was as if the TXV was tracking but overshooting/overcompensating way faster than anything I've ever seen. I ended up putting some ports at the air handler and ended up with different pressures and temps altogether.
    It was impossible for me to see what kinda temp difference I had from the cond unit to the air handler with my lineset since the pressures where going up and down so fast.
    To make matters harder to find.... they started out with 3/8ths at the unit, spliced in 5/16 under house, then made another splice before it got to the air handler. So at first glance, it looked like it was the right size hehe.
    [Edited by wormy on 03-28-2005 at 09:58 PM]
  11. #37
    To Dash 3-28-05
    You write about a sensing bulb on the TXV line. What does it look like and where is it attached? I'll look myself.
    The Bryant dealer/distributer tech refuses to come out to check my system. He insists that I get someone else to come out and if that man finds something wrong, then the Bryant dealer will come out and fix it.
    I'm sure that's a good bet for him judging by the number of techs who answered this thread and said there was nothing wrong my system. Only about 90 percent of the tech posters indicated that they felt that there were ways to check and possibly solve my desire for better dehumidification by checking the sensing bulb and sub cool and super heat. About 50 percent said that the system was dehumidifying fairly well, but should be checked to see if it working at peak performance as expected.
    If I hire a new tech, I could unluckily hire someone who didn't believe in or know how to check sub cool or super heat or not be interested in how the sensing bulb is attached to the line as Golan37 noted I should check in his post.
    The Bryant dealer tech is probably counting on the latter.
    The Bryant dealer tech came out to my house one time only to check the system in July 2004 and recharged the system. He checked no "bulbs" or "super heat or sub cool". He insisted that there was no way to check anything other than refrigerant pressure.
    Today, someone who read this HVAC site thread apparently mentioned to him that I was seeking info on this site.
    He, the Bryant dealer tech, wrote the e-mail shown below to me today.
    As you'll note in his e-mail he says now that "super heat can be checked but not adjusted".
    It is sad that the problematic Bryant dealer tech only read the posts on this site that say I have no problem with a system that on the warmest most humid days can only bring the humidity down to 48-50 percent. Some posters on this HVAC site said "50 percent is good enough".
    One of the kind posters on this site posted a link to Carrier humidity chart that clearly showed that Carrier's advertised "ideal humidity" is 40 to 60 percent, and that Carrier can reach those values. My system can only dream of 40 percent even when the humidity outdoors is only 50 percent.
    I kept a log of temp and humidity for many days during July and August 2004. The lowest that I ever got my house to was 48 percent humidity at night.
    I only want the performance that I bought!!
    Unfortunately the Bryant Dealer believes that what the customer wants is irrelevant, even if the Bryant/Carrier literature promises 40 to 60 percent humidity levels in the home.
    As I wrote to lcimpala65, I don't want to use this info that I get on this site against the dealer. I want to try to understand my problem so that I can convince the dealer tech to do what should have been done last year.
    I just want it fixed. I previously had a system for 34 years. I never had one problem in all those years.
    This is the e-mail I got from the Bryant tech today.
    To: <RHBLAKE57@COMCAST.NET>
    Sent: Monday, March 28, 2005 5:08 PM
    Subject: R410A
    > DICK
    > I READ YOUR QUESTION ON HVAC TALK IT SOUNDS LIKE MOST PEOPLE AGREE
    > WITH ME. HOWEVER I DID NOT SAY YOU CAN NOT CHECK SUPER HEAT I SAID YOU CAN
    > NOT ADJUST IT. WHEN WE RECHARGED THE SYSTEM WE DID NOT PUT BACK WHAT WE
    > TOOK OUT WE MEASURED THE LINE AND ADDED THE CORRECT AMOUNT FOR YOUR
    > SYSTEM ACCORDING TO YOU PIPING LENGTH THEN CHECKED IT WITH THE CHART LIKE
    > I SHOWED YOU. THERE IS NOTHING WRONG WITH YOUR SYSTEM YOUR DUCT IS
    > NOT LEAKING ENOUGH TO CAUSE A PROBLEM BUT ALL DUCT SHOULD BE SEALED
    > AGAINST ANY LEAKAGE WITH DUCT SEALER I DO NOT KNOW IF B&B DID THIS I WOULD
    > HOPE THEY DID. AGAIN IF SOME ONE COMES UP WITH SOME THING I WILL BE GAD TO
    > COME OVER AND TALK WITH THEM.
    > SCOTT
    Thank you Dash for your help
  12. #38
    Apr 2003
    Cullman Alabama,
    Thumbs down
    I have to ask: what do you expect to achieve by continuing to post here? A lot of the techs on this site have given you all kinds of things to "check". Not one of them said you actually have a problem, some said they "think" it should do better, but this is based on what YOU are telling them. They have no way of knowing if what you percieve as happening is actually happening or not. Now these techs on this site are very knowledgable, can they fix your system for you? NO they can't. All they can do is give you , a bunch of check this and that, all of which your installing contractor could have already checked.You base your humidity readings on your own equipment which you say is calibrated. Calibrated by whom? how often? It is taken to a calibration lab every six months? I doubt it. I still say you don't have a problem. It makes NO sense at all that a contractor would ignore you UNLESS he has TRIED to please you and has found that there is NO pleasing you. Just a side note congrats on your years as a salesman. But to be fair, cookware won't come close to the trouble a homeowner can dream up about his heating and air system. I'll tell you what, have your contractor come over and run a PSYCHROMETRIC analysis on your system, it will tell you exactly how much cooling you are getting and exactly how much humidity is being removed from the air. If the analysis shows your system to be performing poorly than you have something to complain about. If it shows that your 2.5 Ton is doing all it can do then thats it. If it shows a problem then the contractor should fix it, or explain why it can't be fixed without more of your money fixing it. Good luck.
    [Edited by lcimpala65 on 03-29-2005 at 07:16 AM]
  13. #39
    Apr 2002
    You posted 48% previously and that is below 50.
    What were you measuring the humidity with on the old system when you were claiming 38% humidity?
    38 sounds unrealistic to me.
    http://www.ductstrap.com/