Hello everyone, went to a call today on a ICP heatpump
Model PH 5542AKA5 Package system. Installed Dec.03 by the owners relative. Problem breakers tripping when CC is energized after checking and isolating problem to the compressor , realized comp. is stuck, ohm compressor checks good , Check to ground no shorts. Just seems to be locked up. Just wondering has anyone out there seen this problem very often.
-
03-23-2005, 03:19 PM #2
Professional Member
- Join Date
- Nov 2004
- Posts
- 2,923
Did the internal overload not open?
It just threw a breaker?You might get it unstuck.
I dont see that often.
-
03-23-2005, 03:50 PM #3
Regular Guest
- Join Date
- Oct 2003
- Location
- arkansas
- Posts
- 8
Thanks for the reply Jacob , but no the overload didn't open, I wish it would have . When I first went to this call noticed the breakers were not properly wired for correct amp loads the customer had 80+ amps ( 2 heat strips and condenser loads) all wired into a 50/50 breaker. Thinking this might have been the culprit in the tripping of the 50/50 I unhooked a third strip from an isolated 30/30 breaker . And ran the condenser load directly to it. Unhooked my Comp. common from the CC (to isolate the OFM ) Everything came up fine (fan runs) good amp. draw. But soon as Comp. common is tied back in WALA 30/30 trips just like 50/50.
-
03-23-2005, 07:40 PM #4
I carry a kickstart booster, for use on stuck compressors.
Most of the time it will free them.
Then when i check the charge, I usually find it was over charged and is washing out the oil.
Redo the charge and they some times run for years, other times for weeks.
A running amp check gives you a good idea how long they'll last.