    is there any way to make a furnace work right in a house if it is about 50,000 BTUs oversized?-- need some more professional opinions for a homeowner.

  2. #2
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    Post Likes
    Tear it out and install the correct size.
    How tall are you Private???!!!!

  3. #3
    Join Date
    Apr 2004
    Posts
    420
    Post Likes

    Wink

    Put an addition on...

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    leave the windows open

  5. #5
    Join Date
    Dec 2003
    Location
    Location!, Location!
    Posts
    930
    Post Likes
    MORE as in number or in quality of opinions?
    This is a loaded post- Who has determined the oversized condition? What, if it is so, is the correct size relationship(in other words, is 50K a 50% oversizing or a 25% oversizing or what?) Why is the unit oversized? Why isn't the first thought to replace with the correct size, will there be expansion in building? If this is a new install, why not get the installer by the short ones, and get satisfaction? If these factors don't concern you, then just load that sucker up-open all the windows, punch holes in the roof, etc.

  6. #6
    Join Date
    Feb 2005
    Posts
    29
    Post Likes
    Thread Starter
    well, a 90000 would suit his needs perfectly. He bought this and installed it. thought bigger was better,I went there to see why it was recycling all the time, burner shutting off and then the blower running for about 6 min, then off, then on and so on until the exchanger cooled, I just told him that the unit was grossly oversized for his needs. He would have to pipe hot air to the outside and cold air in side to equalize the thing, they don't believe me. this unit would easly heat 2 houses like theirs.

  7. #7
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Is this an oil furnace by chance? If so, downfire the nozzle size and run the blower on low speed. You could even adjust the fan and limit settings to accomodate less cycling. Don't go to low on nozzle size or consumption will likely skyrocket and exhaust temps will be too low.




  8. #8
    Join Date
    Feb 2005
    Posts
    29
    Post Likes
    Thread Starter
    yes oil burner, i slowed the fan and set the limits to 90 and 130, from 120 and 150.. I did suggest changing nozzels from 1.00-80B to 85-80B.They also need more- larger ducts, hot and cold. it's just hard to get it through to them.

  9. #9
    Join Date
    Feb 2004
    Location
    chicago suburbs
    Posts
    4,422
    Post Likes
    Originally posted by oilie hands
    yes oil burner, i slowed the fan and set the limits to 90 and 130, from 120 and 150.. I did suggest changing nozzels from 1.00-80B to 85-80B.They also need more- larger ducts, hot and cold. it's just hard to get it through to them.

    tell them what it needs and walk away. you don't need the headache.
    FILL OUT YOUR PROFILE!!

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Down fire it to .75, and adjust the blower to the middle of the units rated temp rise.

    Other then that, they screwed themselves.

  11. #11
    Join Date
    Jul 2001
    Location
    Delaware
    Posts
    1,232
    Post Likes
    Be careful in downsizing the nozzle. Don't drop below the minimum for the installed end cone if it is a Beckett burner.
    Work is for people who don't know how to fish.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Originally posted by GradyWhite244
    Be careful in downsizing the nozzle. Don't drop below the minimum for the installed end cone if it is a Beckett burner.
    Hate when I forget those details.

    Thanks Grady.

  13. #13
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Originally posted by oilie hands
    .... i slowed the fan and set the limits to 90 and 130, from 120 and 150..
    I would have reset the limits to 100, 170, 200 instead. With these settings you'll have 70° of limit span which will reduce fan cycling. Brief rundown of each setting has 170° being the fan turn-on temp, 200° being the max plenum temperature (burner high limit) and 100° being the blowdown temperature after the thermostat is satisfied. I usually use these settings on all units, including new installations, since HO (including myself) hate short fan cycling.

  14. #14
    Join Date
    Oct 2002
    Location
    Mahopac NY
    Posts
    448
    Post Likes
    Lets go back to plan A... Do a heat calc, rip it out, and install a correctly sized unit.
    Dogs truly are man's best friend!!

  15. #15
    Join Date
    Feb 2005
    Posts
    29
    Post Likes
    Thread Starter
    UPDATE, first I have to say this, some people can not trot out and buy a new furnace, car or whatever everytime a serviceman or mechanic tells the to, sometimes spending a couple hundred trying to fix something suits their wallet better than spending a couple grand plus buying new.
    Here's what i done and they should get a good many safe years out of their unit.
    I took out the 1.00-80 and replaced it with an .85-80 and had the option of going down to .70. I took out a cold air return duct that they had in the basement 10 feet from the unit, patched the hole and ran a hot air duct to an unheated entrance room away from the furnace.
    I told them to keep the door that leads down to the basement closed, they left it open to relieve some of the heat from their big unit, now the basement is a nice 60 degrees.
    CO2 11%-unchanged
    draft .025 from .050
    stack 420 from over 600
    have the fan limit on at 160 and off at 100
    heat rise is a little high --about 90 should be 85 or under.
    efficiency about 83%
    cost to heat for the next yr--unknown.

  16. #16
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    When you changed the nozzle to a smaller size, you did adjust the amount of air, right?

    The other thing found strange, to me at least, was the draft decreasing when the smaller nozzle was used. Are you checking the draft when the burner is running at the breach?


  17. #17
    Join Date
    Feb 2005
    Posts
    29
    Post Likes
    Thread Starter
    yes, draft is .025 at the box and at the flue.
    air was 0, now is open about 3/16"
    there is enough draft to suck your hat off, it's an 8' flue going into an 8X12 chimney, should be a six inch flue for the smaller nozzel

    [Edited by oilie hands on 03-26-2005 at 01:23 AM]

  18. #18
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Originally posted by oilie hands
    air was 0, now is open about 3/16"
    That makes it sound like you opened the air, from zero to 3/16".....probably the other way around if you installed a smaller nozzle. You should be using the side disk to adjust air on the Beckett burner as well, not the larger band. Small firing rates should use the disk for adjustment, it promotes better burning (says Beckett anyways).


    Originally posted by oilie hands
    ....there is enough draft to suck your hat off, it's an 8' flue going into an 8X12 chimney, should be a six inch flue for the smaller nozzel
    Chimney size doesn't have to be sized to the firing rate, that's what the draft regulator is there for. Open that while the burner is running steady-state to obtain -0.02" WC over the flame. More draft never hurts, but cuts efficiency.....too little draft and the fire suffers and can even burn the end cone Becketts are known for.



    [Edited by oilie hands on 03-26-2005 at 01:23 AM] [/B][/QUOTE]

  19. #19
    Join Date
    Jul 2001
    Location
    Delaware
    Posts
    1,232
    Post Likes
    Originally posted by casturbo

    The other thing found strange, to me at least, was the draft decreasing when the smaller nozzle was used. Are you checking the draft when the burner is running at the breach?
    I noticed that too but then when I saw the drop in stack temperature, I realized less heat up the chimney = less draft. I don't remember seeing any smoke or CO numbers. Often when you reduce nozzle size, CO goes way up. Not trying to be picky, just cautious.
    Work is for people who don't know how to fish.

  20. #20
    Join Date
    Feb 2005
    Posts
    29
    Post Likes
    Thread Starter
    it pays to be questioned and picky when playing with fire.. thanks
    heat rise is about 80
    CO2-11 CO-6
    my old eyes and glasses saw between 0 and 1 smoke
    younger eyes said 0, i didn't argue.

    [Edited by oilie hands on 03-26-2005 at 11:53 AM]

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •