Thread: Refrigerant leaked out

  1. #1
    Join Date
    Mar 2005
    Posts
    1
    Post Likes
    I am a home owner with a new Trane heat pump. The system developed a leak shortly after installation and as a result, ran for over a month with almost no refrigerant. Would this have done any harm to the system?

    Thanks

  2. #2
    Join Date
    Nov 2002
    Location
    emerald city, sc
    Posts
    1,469
    Post Likes
    it depends on what was done when the leak was found and repaired. how much refrigerant leaked out. type of refrigerant. how much run time?
    i wanted to put a picture here

  3. #3
    Join Date
    Jun 2000
    Location
    WYO
    Posts
    2,187
    Post Likes
    Most new systems dont just suddenly develope a leak,It was probably done during installation .If the system was evacuated with a leak,you have air and moisture in the system. You may have other probs as well now.
    Hopefully the problem was followed up and corrected ASAP,correctly. If not solved correctly, you may have problems.

  4. #4
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Originally posted by john999
    I am a home owner with a new Trane heat pump. The system developed a leak shortly after installation and as a result, ran for over a month with almost no refrigerant. Would this have done any harm to the system?

    Thanks
    I would say it ran for over a month with a slowly diminishing amount of refrigerant.

    If it was a large leak and the charge blew quickly, the compressor would've likely gone out on internal protection and you would've noticed the loss of performance quickly rather than gradually.

    Nevertheless, a proper repair to the leak, new liquid line drier, and evacuation to 500 holding-steady-at-blank-off microns is called for before the system is recharged and returned to service.

    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  5. #5
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    And buy the extended warranty, if it is offerred.
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  6. #6
    Join Date
    Apr 2004
    Location
    Niantic, Illinois
    Posts
    545
    Post Likes
    If it was a model better than the entry level builder's model it will have high and low pressure switches to protect the unit. So if it was one of the middle end or higher units it probably leaked slowly. Most likely the leak was there from the beginning. The Trane units that are leaking from the installation are usualy leaking at the evaporator end. There is a compression fitting on the liquid line side that the installers don't always properly tighten. Also the suction lines are a bit tough to braze at the evap coil, they tend to have a tiny hole on the bottom of the joint. My personal theory is that this leak is caused by the soft solder that Trane uses to put the cap on the end of the tubing. After you heat it up to pop the cap off it settled in the bottom and causes the braze joint to not take well. I always braze with nitrogen. Then I pressurize the system with nitrogen to 150 psi(the max my regulator goes) and use big blue to check all of the fittings and joints. It works very well for me.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •