Thread: Carrier FE4 cond. pump tie in ?

  1. #1
    Join Date
    May 2004
    Posts
    58
    Post Likes
    Contractor #1 installed 2) Carrier FE4 infinity fan coils.
    The low voltage saftey of the condensate pumps are not tied in (I found out when the 2nd floor flooded last summer)
    Fired #1 (no insurance), units installed and up and running

    Contractor #2, Hired him to come in and check the charge on the units and check over the install, $900.00 later, and He does not se how the condensate low voltage can tie into the FE4's Board.

    Contractor #3 - he does not know.

    So how does the Condensate low voltage "cutout" tie into the Infinity system. I have all the manuals (tech and owner)
    and it never mentions the condensate pump ??

    Thanks,
    Nick

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Normally you break either the power to the thermostat or if cooling only, break the signal to the outdoor unit. I would think that would still be possible but dash, our Infinity fan, better confirm.

  3. #3
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    It's one thing ,that Infinities designers overlooked.It can be done though it will cut all low voltage to the control,and provide no display of the problem.

    There are 4 wires,two are digital signals for controls,the other two are the 24v power,so you wire it to break the 24 volts.If I remember correctly it's best to interupt "D",double check to diagram to be sure.

    If you don't have two speed outdoor units,you can interupt the compressor contactor to the outdoor unit from the air handler.But if it's a two speed compressor the signals are digital,no way to interupt ,so break the 24V.

    Maybe the next generation will address this in a better way.

  4. #4
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Break D to UI. Kills it all. H/O will know there's an issue at that point.

    Oh, ya...I'm back...learning to overlook the stupid posts.

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Originally posted by jrbenny
    Break D to UI. Kills it all. H/O will know there's an issue at that point.

    Oh, ya...I'm back...learning to overlook the stupid posts.

    Gald you're back,value your opinions,need a little more "deep blue" around here.

    Now tell how the SM's meeting in Florida went!LOL

  6. #6
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    Bout time your back. Thpought our "local" lad said somethng about breaking the communication line w/ single speed outdoor and D w/ tdb/ydb

  7. #7
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    oh, and for my brothrs in arms, Carrier has came out w/ a wonderful manual, it has all the heat wave, puron, inf, zone, it is the bible now a days
    great book, give it to my techs and i use one to,
    lot of gray matter you know.

  8. #8
    Join Date
    Mar 2003
    Location
    Idaho
    Posts
    196
    Post Likes
    Originally posted by htinglky
    oh, and for my brothrs in arms, Carrier has came out w/ a wonderful manual, it has all the heat wave, puron, inf, zone, it is the bible now a days
    great book, give it to my techs and i use one to,
    lot of gray matter you know.

    Got any more info on that manual such as a number or a
    title? Is it available for downloading @ the partners site?

  9. #9
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    dont know about partners but it is a few hundred pages so I suspect it wouold take awhile.
    Got ours from our local carrier rep,
    We affectionaly call it the blue bible

  10. #10
    Join Date
    Mar 2003
    Location
    Idaho
    Posts
    196
    Post Likes
    Thanks, I'll check w/ our distributer Monday.

  11. #11
    Join Date
    Mar 2001
    Location
    Kill Devil Hills, NC
    Posts
    217
    Post Likes
    How about sharing that catalog number?
    mcair

  12. #12
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    not a catalog number associated with it. something that we put together locally. All current pdf's for service/install on residential products in one binder.

  13. #13
    Join Date
    Feb 2003
    Posts
    275
    Post Likes

    Talking

    It didnt have one on the book, I will ask Jrbenny to post monday when I see him w/ the #

  14. #14
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    I will type in all the Cat numbers tomorrow so you all can see them.
    Rob what about the warrenty page?
    Dash, are you any where's close to Fort Meyers?
    My daughter and son in law are talking about buying a house and I want a good carrier rep to take care of them.
    Thanks

  15. #15
    Join Date
    Jan 2005
    Posts
    27
    Post Likes

    Talking

    you can wire in the safety to the 24 volt transformer before it gets to the air handler board. Iwould also recommend one of the wagner wet switches since the P traps always clog before the pumps do ,they work well. again these go in the wiring before the infinity control board

  16. #16
    Join Date
    Apr 2004
    Location
    Niantic, Illinois
    Posts
    545
    Post Likes
    Originally posted by htinglky
    I will type in all the Cat numbers tomorrow so you all can see them.
    Rob what about the warrenty page?
    Dash, are you any where's close to Fort Meyers?
    My daughter and son in law are talking about buying a house and I want a good carrier rep to take care of them.
    Thanks
    Charlie Greer lives in Ft. Meyers. If you go to his web site http://www.profitboosters.com there is an email link there. He can put you in touch with cream of the crop.

  17. #17
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    thanks

  18. #18
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    mvp trouble shoot #535-80083
    mvp start up/install #535-80110
    service/maint mta #535-80098
    " " mxa #535-80099
    Inst, start up, ops and ser cva # form 58CV-3SI
    CVA troubleshoot #535-80107
    AHU ser manual #03FA-4A3
    Inst, start up, ops and ser sta/stx form 58ST-11SI
    " " " " " dla/dlx Form 58DL-3SI
    " " " " " cta/ctx Form 58CT-4SI
    puron app guide,ser man 533-781 (FE AHU #63FE-4A0)
    R22 " " " " 563-732
    thermidistats 03TS-TA17
    " Wiring 03TS-TA18 thats all folks!
    programable 03TS-TA2
    duel fuel (my favorite) 03TS-TA9
    Non prog 03TS-TA5
    Infinity, install, sraet up 809-50020
    " zone 809-50025
    " net innerface 809-50015

  19. #19
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Originally posted by htinglky
    I will type in all the Cat numbers tomorrow so you all can see them.
    Rob what about the warrenty page?
    Dash, are you any where's close to Fort Meyers?
    My daughter and son in law are talking about buying a house and I want a good carrier rep to take care of them.
    Thanks

    Ellsworth Htg & Cooling,William Barnes,239-995-6005


  20. #20
    Join Date
    Feb 2003
    Posts
    275
    Post Likes
    thank you

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •