Results 1 to 13 of 35
Thread: What makes compressors fail
03-16-2005, 10:39 AM #1
- Mar 2005
- 32
What is the number one cause for compressor failure.
03-16-2005, 10:45 AM #2
Human error.
03-16-2005, 10:50 AM #3
Compressors don't die; they're murdered.
Number One cause of compressor failure: improper installation procedures. This encompasses a long list of things: improper evacuation, not sweeping the lineset with nitro during brazing, no liquid line drier, ductwork improperly sized, system improperly sized, OVERCHARGE, improper piping procedures, etc.
Runner up is improper maintenance, even on a properly installed and sized system. Dirty coils, poor service procedures, etc. will put a compressor on death row as quick as anything."In this house we obey the laws of thermodynamics!"
- Homer Simpson
03-16-2005, 11:35 AM #4
- Nov 2001
- 1,874
Electricity being applied,
They don't fail till they are energized.If you try to fail, and succeed.
Which have you done ?
03-16-2005, 03:25 PM #5
For me, the number one cause of existing compressor failure is low freon levels.
2nd cause would be liquid getting to compressor.
Wonder why anyone would think to answer about a new install ?? Only had two compressors in thirteen years fail that we installed. And one of those was in a low-rent apartment complex.The other was a 12 Seer system.
03-16-2005, 04:37 PM #6I must commend you on your low failure rate in systems you've installed. Sounds to me like you're doing things right if that's the case.Wonder why anyone would think to answer about a new install ?? Only had two compressors in thirteen years fail that we installed. And one of those was in a low-rent apartment complex.The other was a 12 Seer system.
Why did I respond as I did regarding installs? I didn't just have new installs in mind, but repair/replacement efforts as well. If a system isn't sized and installed right, the compressor will pay for it, sooner or later. Bad repair efforts also can jeopardize a compressor's life. Once I bothered to investigate why compressors fail, I have yet to find one that's the fault of the manufacturer.
I also think overcharged systems are a larger culprit in compressor failures than undercharged, as an undercharged system is more likely to see the compressor kick out on IP, even under lighter loads, which would draw attention to itself faster (an undercharge usually means there's a leak, which also calls attention to the system). An overcharged system might kick out only under extreme conditions but otherwise run a greater percentage of time under potentially floodback conditions, which is anathema to valves and lubrication of a compressor.
Electrical failures account for another percentage of comp failures, ranging from single phasing of three phase compressors, to inadequate voltage supplied to a unit, to dirty contactor points, etc. The latter two I mentioned might be a result of installation or maintenance effots. Undersized wiring and no regular inspection of electrical components would contribute to a failure.
[Edited by shophound on 03-16-2005 at 04:39 PM]"In this house we obey the laws of thermodynamics!"
- Homer Simpson
03-16-2005, 04:47 PM #7
Shop
Did not mean anything offensive !
Have just heard a lot of threads that indicate compressor falures on fairly new systems.
And I did not think of it the way you did, as i don't see many failures that I can blame on the system. Although there are a few.
MOst times, around here, if the freon is low, the HO does not realize anything except he is not cooling, and then some time later decides to call for repair. By the time he has called and I arrive, the unit has been on a long time ( maybe even over the weekend ), the compressor has overheated & shut off, cooled down & run again, several times before I get there. I do try to remember to tell them to shut it off, but sometimes I forget.
And around here, filters & coils get real dirty, but the HO doesn't know it until his cooling has stopped. By that time, liquid has gotten to the comprssor more than one time, before he calls it in.
03-16-2005, 05:04 PM #8
Member
- Mar 2003
- 1,877
flooding - caused by small return air, overcharge etc..,
03-16-2005, 05:18 PM #9
compressors normaly dont burn out
human error is the bigest cause for failed copressor
03-16-2005, 05:18 PM #10None taken. Just wanted to clarify.Shop
We're cool.
You have a good point about homeowners being slow to call in a unit that's undercharged and has a compressor that's cycling on IP. I work on commercial stuff that I'm directly responsible for so I tend to forget the homeowner factor when I post!
Your last paragraph falls within my "runner up" catagory of poor maintenance. So, I guess we could say that perhaps a leading cause of compressor failures in the residential sector is, well, homeowners!
- Homer Simpson
03-16-2005, 05:25 PM #11
Shop
Residentially speaking: You are absolutley right at least in this area. Most compressor failures that I see are HO induced.Of course a lot of these are rentals or apartments.
Done by tenant ( or not done as the case may be )
Look forward to bantering with you again !
Richard
03-16-2005, 05:39 PM #12
#1 Cause of Comp. Failure.
Here's my story: 1. Luxury Apartment Complex
2. 128 Apartments
3. 4 Bozo installers
4. 1 mildly warm Indiana summer
5. 24 (yes, 24) comp. replacements
6. 1 extremely mad boss
One co-worker actually said "Hmmm, must have been a bad batch of compressors at the factory." We have a new company policy about installing air conditioners now. So sad it took something like this to make it come about.
03-16-2005, 06:59 PM #13I like thatOriginally posted by shophound
Compressor failures within the first year are usually caused by improper installation, application or just plain old bad work habits.
Compressors that go for more then a year are usually killed by overcharging. Most overcharging is due to improper diagnosis of symptoms. Most units that are grossly overcharged are done by techs who only read suction line data. Low suction caused by low indoor air flow due to dirty filters and/or coils are misconstrued as low refrigerant. Adding refrigerant brings the superheat of a system with low indoor airflow back to normal and allows the system to operate but with a reduced capacity and with possible slugging of liquid back to the compressor.Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
