Thread: Ruud Furnace stumps Pros

  1. #1
    Join Date
    Mar 2005
    Location
    Mission BC Canada
    Posts
    8
    Post Likes
    I look after an elderly widow (84) who has had a lot of trouble with her 1990 Ruud UGDA- 10ECBEA HIS furnace. I am not in the HVAC trade, neither am I a DIY or a DYI I reside near Vancouver British Columbia Canada. I have hired pro contractors to do the job, but after three different contractors, the latest solution suggested is to replace the furnace. Considerable dollars have already been spent $1700 in repairs with reputable companies.
    Parts Replaced:
    Nordyne HIS 903758 Mar. 31, 2004
    Millivolt thermostat Oct. 01, 2004
    Main Gas Valve Honeywell VR8Z45M2530 Dec. 30, 2004
    Relay switch for control Dec. 30, 2004
    Time Delay control Jan. 31, 2005
    Control module (board) Feb. 2005
    Control module (board) Mar. 2005

    After the control module has been reset (by power off) the furnace will cycle through the start up sequence and fire the burners, blow heat, burners shut down, relight and blow heat and shut down and fault with no restart unless the power to the furnace is cut and the control module reset. This has stumped the contractors who have tried diligently to fix the problem.

    In desperation I brought over a electronic technician friend of mine to take some measurements, he has 25yrs in circuit boards. When the control module faulted it was intermittent, sometimes it would kick 24v to the gas valve but not open it, or at other times no volts were sent to the gas valve. This control module has been replaced twice in two months and it appears to be faulty again. Should I have this replaced again? Any suggestions other than a new furnace.

    Control Module: Robertshaw HS780 34NL-306A Part # 100-00812-31

  2. #2
    Join Date
    Apr 2004
    Posts
    158
    Post Likes
    Why would they put a millivolt t-stat on a 24v system?

  3. #3
    Join Date
    Mar 2005
    Location
    Mission BC Canada
    Posts
    8
    Post Likes
    Thread Starter
    Not sure why the tech did that, I don't even know were it’s located. I think the tech was trying in desperation. The company he works for sent a tech from another company that was supposedly a Ruud expert. That is when the second control module was put in. The tech that gave up on this repair suggested that a flame rod sensor be put in??

  4. #4
    Join Date
    Apr 2004
    Posts
    158
    Post Likes
    Originally posted by hamish
    I
    After the control module has been reset (by power off) the furnace will cycle through the start up sequence and fire the burners, blow heat, burners shut down, relight and blow heat and shut down and fault with no restart unless the power to the furnace is cut and the control module reset. This has stumped the contractors who have tried diligently to fix the problem.


    Control Module: Robertshaw HS780 34NL-306A Part # 100-00812-31

    What is the fault code on the circuit board?

  5. #5
    Join Date
    Mar 2005
    Location
    Mission BC Canada
    Posts
    8
    Post Likes
    Thread Starter
    The circut board has no fault code LEDs on it.

  6. #6
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes

    There is no furnace problem that a real professional heating and cooling technician can't properly troubleshoot given the time and proper instrumentation. If you had a true professional technician out, the problem would have been taken care of already.

    Call another service company. Have the technician contact the factory's tech services department if necessary. The problem can be solved.

  7. #7
    Join Date
    Mar 2005
    Location
    Mission BC Canada
    Posts
    8
    Post Likes
    Thread Starter
    Thanks for the encouragement that the problem can be solved. My elderly friend is quite distraught over this and feels that she needs to buy a new furnace. Does the symptoms I describe sound like the control module again? If so I think it must be under warranty and maybe I should get the tech back to replace it.

  8. #8
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    Have the technicians troubleshoot by jumpering the R to W terminals at the furnace? That would eliminate the thermostat and thermostat wiring as the source of problem.

  9. #9
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    There is no way for any of us to troubleshoot the problem without actually being there. If the others who were there could not determine the cause we are at an even greater disadvantage.

    It could be the control and it may not be. The control monitors safeties and other functions. There are inputs to the control from all sorts of sensors and control components. The control is the brain of the system. It will shut down if any of the sensors detect a problem. So, it could be that the control is doing exactly what it is supposed to do and the problem is elsewhere. It could also be the control itself. If I were there I could find the problem.

    You need to find a real professional to solve the problem. One who knows what he is doing and will not give up easily.


  10. #10
    Join Date
    Mar 2005
    Location
    Mission BC Canada
    Posts
    8
    Post Likes
    Thread Starter
    Thanks for your advice. It's hard to find a real professional, when you call the ones listed they all say That they are professionals. I have tried 3 now with no luck yet. Is there some sort of testing equipment that only a true professional would have that I could maybe ask if they have to help seperate the pros from the wanabees?

  11. #11
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    I see that you are located in Mission BC, Canada. Perhaps someone on this board will read this who runs service in your area and may be willing to work with you.

    Norm

  12. #12
    Join Date
    Mar 2005
    Location
    Mission BC Canada
    Posts
    8
    Post Likes
    Thread Starter
    Good idea Norm. Thanks for your help.


  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Have check the limits, and the pressure switch also.

    Your electronics friend may know electronics, but you need to know the sequence of operation when trouble shooting.

    And get rid of that millivolt t stat.

  14. #14
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    there are many reasons for a control to lockout first i would forget warrenti on the control it seems they are guessing and if you cant fix it replace it seems to be the way they work. we are at a major disavantage on this one hard to say what it is without being there. robershaw did have problems with thier control at one time but they resolve the problem a few years ago so chances are you didnt get one with the problem. i am about to go against something i said in an earlyer post on an other page hehehehe. look for a nate cirtified co with a nate heat tech. this should not be to hard to resolve if the tech has the correct tools. change that milivolt stat first

  15. #15
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    my bet would be that their is not a flame sensor on that unit. that vintage used the ignitor only to sense flame and it does not do it very well. thier is a "remote flame sensor kit" available that updates it to use a sensor. you can tell if it has one because their will be a metal rod bent at a 90 degree angle on the burner farthest away from the ignitor. the sensor will have a red or orange wire attached to it.

    lemme know

    kgod
    ...

  16. #16
    Join Date
    Jan 2005
    Posts
    27
    Post Likes

    Talking

    have them check the gas pressure before the furnace ,most need at least 4" of w.c to operate ,turn on all the other gas appliances during this test so you can seethe lowestit goes.call gas company to adjust the meter up if it falls below 4". i also ran across a ruud furnace that had apressure switch that was sticking closed at times since no diagnosticlights it acted as if the board was dead , no operation with input to the board. as noted before get rid of the millivolt thermostat. hope this helps

  17. #17
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    The first 2 repairs were wrong if you've got them right.
    Nordyne igniter on a Rheem furnace, amperage might be differant.
    Millivolt thermostat on 24v furnace.
    Either wrong part could cause board failure, any way you shouldn't have to pay if the first replacement board failed in the first year, and shouldn't have to pay if it failed again - its under warranty.
    $1700 you could have a new furnace.
    You may in fact need a new furnace, a bad heat exchanger can cause the burner to shut down when the blower comes on.
    Ask them to check gas pressure, temp rise, and use a combustion analizer.

    [Edited by rsmith46 on 03-13-2005 at 11:51 PM]

  18. #18
    Join Date
    Jan 2004
    Posts
    214
    Post Likes
    is the furnace & elect system properly grounded?

  19. #19
    Join Date
    Jan 2004
    Posts
    9
    Post Likes
    The suggestion about disconnecting the thermostat and jumping from R to W was the first thing you should try. Does the furnace have a good ground?? Has anyone checked the vent pressure switch? One and One is not making two on this furnace. Should you need to contact Rheem /Ruud (service department) the number is 501-646-4311

  20. #20
    Join Date
    Apr 2004
    Location
    Niantic, Illinois
    Posts
    545
    Post Likes
    Normchris, have you ever taught for ISL in the Wheeling Illinois area?

Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •