    What is the number one cause for compressor failure.

  2. #2
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Human error.
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Compressors don't die; they're murdered.

    Number One cause of compressor failure: improper installation procedures. This encompasses a long list of things: improper evacuation, not sweeping the lineset with nitro during brazing, no liquid line drier, ductwork improperly sized, system improperly sized, OVERCHARGE, improper piping procedures, etc.

    Runner up is improper maintenance, even on a properly installed and sized system. Dirty coils, poor service procedures, etc. will put a compressor on death row as quick as anything.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  4. #4
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes
    Electricity being applied,

    They don't fail till they are energized.
    If you try to fail, and succeed.
    Which have you done ?



  5. #5
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,461
    Post Likes
    For me, the number one cause of existing compressor failure is low freon levels.
    2nd cause would be liquid getting to compressor.

    Wonder why anyone would think to answer about a new install ?? Only had two compressors in thirteen years fail that we installed. And one of those was in a low-rent apartment complex.The other was a 12 Seer system.

  6. #6
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Wonder why anyone would think to answer about a new install ?? Only had two compressors in thirteen years fail that we installed. And one of those was in a low-rent apartment complex.The other was a 12 Seer system.
    I must commend you on your low failure rate in systems you've installed. Sounds to me like you're doing things right if that's the case.

    Why did I respond as I did regarding installs? I didn't just have new installs in mind, but repair/replacement efforts as well. If a system isn't sized and installed right, the compressor will pay for it, sooner or later. Bad repair efforts also can jeopardize a compressor's life. Once I bothered to investigate why compressors fail, I have yet to find one that's the fault of the manufacturer.

    I also think overcharged systems are a larger culprit in compressor failures than undercharged, as an undercharged system is more likely to see the compressor kick out on IP, even under lighter loads, which would draw attention to itself faster (an undercharge usually means there's a leak, which also calls attention to the system). An overcharged system might kick out only under extreme conditions but otherwise run a greater percentage of time under potentially floodback conditions, which is anathema to valves and lubrication of a compressor.

    Electrical failures account for another percentage of comp failures, ranging from single phasing of three phase compressors, to inadequate voltage supplied to a unit, to dirty contactor points, etc. The latter two I mentioned might be a result of installation or maintenance effots. Undersized wiring and no regular inspection of electrical components would contribute to a failure.

    [Edited by shophound on 03-16-2005 at 04:39 PM]
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  7. #7
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,461
    Post Likes

    Shop

    Did not mean anything offensive !
    Have just heard a lot of threads that indicate compressor falures on fairly new systems.
    And I did not think of it the way you did, as i don't see many failures that I can blame on the system. Although there are a few.
    MOst times, around here, if the freon is low, the HO does not realize anything except he is not cooling, and then some time later decides to call for repair. By the time he has called and I arrive, the unit has been on a long time ( maybe even over the weekend ), the compressor has overheated & shut off, cooled down & run again, several times before I get there. I do try to remember to tell them to shut it off, but sometimes I forget.
    And around here, filters & coils get real dirty, but the HO doesn't know it until his cooling has stopped. By that time, liquid has gotten to the comprssor more than one time, before he calls it in.

  8. #8
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    flooding - caused by small return air, overcharge etc..,

  9. #9
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    compressors normaly dont burn out
    human error is the bigest cause for failed copressor

  10. #10
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Shop
    Did not mean anything offensive !
    None taken. Just wanted to clarify.

    We're cool.

    You have a good point about homeowners being slow to call in a unit that's undercharged and has a compressor that's cycling on IP. I work on commercial stuff that I'm directly responsible for so I tend to forget the homeowner factor when I post!

    Your last paragraph falls within my "runner up" catagory of poor maintenance. So, I guess we could say that perhaps a leading cause of compressor failures in the residential sector is, well, homeowners!

    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  11. #11
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,461
    Post Likes

    Shop

    Residentially speaking: You are absolutley right at least in this area. Most compressor failures that I see are HO induced.Of course a lot of these are rentals or apartments.
    Done by tenant ( or not done as the case may be )

    Look forward to bantering with you again !

    Richard

  12. #12
    Join Date
    May 2004
    Location
    Northern Indiana
    Posts
    1,406
    Post Likes
    #1 Cause of Comp. Failure.
    Here's my story: 1. Luxury Apartment Complex
    2. 128 Apartments
    3. 4 Bozo installers
    4. 1 mildly warm Indiana summer
    5. 24 (yes, 24) comp. replacements
    6. 1 extremely mad boss


    One co-worker actually said "Hmmm, must have been a bad batch of compressors at the factory." We have a new company policy about installing air conditioners now. So sad it took something like this to make it come about.

  13. #13
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Originally posted by shophound
    Compressors don't die; they're murdered.
    I like that

    Compressor failures within the first year are usually caused by improper installation, application or just plain old bad work habits.

    Compressors that go for more then a year are usually killed by overcharging. Most overcharging is due to improper diagnosis of symptoms. Most units that are grossly overcharged are done by techs who only read suction line data. Low suction caused by low indoor air flow due to dirty filters and/or coils are misconstrued as low refrigerant. Adding refrigerant brings the superheat of a system with low indoor airflow back to normal and allows the system to operate but with a reduced capacity and with possible slugging of liquid back to the compressor.
    Training is important!
    Practical Training is a must!

  14. #14
    Join Date
    Dec 2003
    Location
    Nevada
    Posts
    1,814
    Post Likes
    Bornriding and shophound read my mind and robo filled in any voids. Other than their reasons I have seen a few compressors fail due to improper 3phase power. For no apparent reason a comp failed and the voltaged were something like 221/222/174 we made a big fiasco and the electricians came in to swap some loads around and do a reassesment.
    Quote
    “Engineers like to solve problems. If there are no problems handily available, they will create their own." Scott Adams

    "We can't solve problems by using the same kind of thinking we used when we created them."
    Albert Einstein

  15. #15
    Join Date
    Jan 2003
    Posts
    540
    Post Likes

    Talking

    Originally posted by geoexchangeman
    What is the number one cause for compressor failure.
    When they don't study for their test.

    What's up with all the credentials?

  16. #16
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    What makes compressors fail ?

    One Word....







    Stress.

    Take your pick, Thermal Stress, Electrical Stress, Mechanical Stress, and Chemical Stress.

    As Shophound said, they are murdered.

  17. #17
    Join Date
    Dec 2003
    Posts
    165
    Post Likes
    Originally posted by docholiday
    What makes compressors fail ?

    One Word....







    Stress.

    Take your pick, Thermal Stress, Electrical Stress, Mechanical Stress, and Chemical Stress.

    As Shophound said, they are murdered.

    I like that answer.

  18. #18
    Join Date
    Mar 2005
    Posts
    32
    Post Likes
    Thread Starter

    Energy

    All these answers are good. The things that make high compressor ratios are the greatest killers. High compressor ratios are the number one killers says the compressor manufactures. Next in line is the wrong voltage either high or low. Flood back of systems with fixed bore metering devices is also up there from over charge. Refrigeration low back pressure unit are made to run with higher compessor ratios. But A/C Units are made to run with high back pressure and therefore lower compressor ratios. So if they are installed and have to operate with less than design air flow they will hit the graveyard quick. I can't leave with out saying a word about Geoexchange. They run with compressor Ratios of less than 2.5 to 1 in cooling some time as high as 3.5 to 1 in heating and have high and low pressure protection. Air source HP unit have to operate with compession ratios of 6 to 1 under normal conditions and let alone the conditions they get in when the HO don't keep the filters and coils clean. Add the defrost cycle, I don't see how the last as long as they do no matter what SEER rating they are. The low end models have only the internal overload to protect them. As I have said geo units love what they are doing and keep on doing it for many years after the warrenty is gone if the HO will just change the air filter. If not the unit will trip out on high or low pressure and must be reset because of the lock out relay. Is that a plus for Geoexchange.

  19. #19
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Originally posted by RoBoTeq
    Originally posted by shophound
    Compressors don't die; they're murdered.
    Adding refrigerant brings the superheat of a system with low indoor airflow back to normal and allows the system to operate but with a reduced capacity and with possible slugging of liquid back to the compressor.
    I think what you meant to say was it brings the suction pressure up to normal but the superheat will go down if you have low airflow and add refrigerant, which will lead to slugging. This is prevented by actually reading superheat and not charging by pressures alone.

  20. #20
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Originally posted by docholiday
    Originally posted by RoBoTeq
    Originally posted by shophound
    Compressors don't die; they're murdered.
    Adding refrigerant brings the superheat of a system with low indoor airflow back to normal and allows the system to operate but with a reduced capacity and with possible slugging of liquid back to the compressor.
    I think what you meant to say was it brings the suction pressure up to normal but the superheat will go down if you have low airflow and add refrigerant, which will lead to slugging. This is prevented by actually reading superheat and not charging by pressures alone.
    In most cases this is correct. I was thinking of one particular instance where the technician made certain that the superheat was correct but ignored the fact that the suction temperature was on 2ºF. In this case, the suction pressure was also low but this tech stuck to his guns and make sure he had the correct superheat. Damnest thing I've seen. The unit was actually operational with solid ice all the way back to and halfway up the compressor housing.
    Training is important!
    Practical Training is a must!

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •