03-15-2005, 06:11 PM #14
Regular Guest
- Join Date
- Nov 2003
- Posts
- 125
I installed real duct in the house I built for myself.
Flex has it's place...just not in my place.
-
03-15-2005, 07:14 PM #15
I never use flex duct as my trunk line.
Will run flex to branch outlets, no problem
If my flex run would be longer than 15 ft, would probably run some 'oversized' hard pipe and then reduce down to flex close to boot.
Flex only used in attic also.
All hard pipe, under house.
And I personally don't like ductboard so I don't use it.
-
03-15-2005, 07:21 PM #16
As already stated flex was originally designed for connection from a metal trunk to a diffuser a few feet away. It does create more of a pressure loss than metal duct so that must be taken into account when sizing. I too am of the less flex the better persuasion.
Quote
Engineers like to solve problems. If there are no problems handily available, they will create their own." Scott Adams
"We can't solve problems by using the same kind of thinking we used when we created them."
Albert Einstein
-
03-15-2005, 07:31 PM #17
Member
- Join Date
- May 2004
- Posts
- 296
flex
I'm an old tin knocker myself but I realize flex has it's place and is here to stay so what is one to say?
-
03-15-2005, 08:53 PM #18
i like flex........just in small doses.
FILL OUT YOUR PROFILE!!
-
03-15-2005, 10:50 PM #19
I like flex too... Cut a piece a few feet long, loop it so one end is pushed inside the other (so it makes a tight circle with no hole in the middle), paint it orange and ya got a pumkin!
I think flex has it's place, but the only place I actually like to use it is on the comercial jobs to hook up the diffusers to the duct, or in some cases in residental where hard piping from the duct to the register would be impossible with out a lot of elbows.
Personally if I have the choice, I never put flex where it can't be reached once the house is done (between floors or other similar places). In attics, I might use a few feet, crawlspaces only if there's absolutely no other way. Our code says 7' max, I try to stick to 3' myself.
-
03-16-2005, 06:28 AM #20
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,255
Replacement system
Review the Manual D and J design.Originally posted by judgetc
I was told by the installer that all the duct will be the flexible type. What do the experts think????
If it does not exist, go onto the next shop.
Suggest to use adequately sized ( ~1,000 FPM) duct header of ~ 2 feet per ton at fan outlet.
i.e. 5-ton, 14"x20" about 10 feet long.
Flex limit of 20 feet on branch runs is good rule-of-thumb'.
Add Simple E.S.P. TEST as part of your contract:
Max. 0.2" in header, withhold 25% of total estimate until static pressure can be maintained at < 0.2". 0.3" if using a variable speed air handler.
[Edited by dan sw fl on 03-16-2005 at 06:54 AM]Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities