What is the standard for temp. difference between supply and return air?
How good can it be?
-
03-12-2005, 04:27 PM #2
Professional Member
- Join Date
- Feb 2004
- Posts
- 2,597
heating or cooling?
cooling 15-20 deg.
heating, whatever the data plate states for a heat rise, shoot for the middle of that range.
if a heat pump as opposed to fossil fuel, then, as a "rule of thumb" which doesn't mean much, in the heat mode without any aux heat running, at 32 deg o.a., the split should be around 20 deg. for every 3 deg. higher, add 1 deg of split temps.
i.e. 35*=21 split.
29*=19 split.
this is not a perfect example, but only a reference.
good luck
-
03-12-2005, 05:06 PM #3
Regular Guest
- Join Date
- Mar 2005
- Posts
- 15
a good temp. is 15 to 20. Why because if it goes to 25 to 30 the evap. coils will start to get frozen.
-
03-12-2005, 06:31 PM #4
Is your heat pump, in the heat or cool mode?
In heat it will vary by the ouotdoor temp.