    Hmm Can't find restriction. Help
    Got a 3 ton ruud unit that won't allow us to charge up properly. The lowside pressure drops to zero psig and the highside goes up to 150 or so. A few seconds later the internal pressure relief valve is heard and the compressor begins to heat up. We have changed both liquid and suction king valves, replaced the filter drier, cut the liquid line at the evp. and blew nitro through the coil and the liquid line it self. We also blew out the metering device. When we did the metering device there was lots of oil. When blowing the system the pressures quickly elevated. This tells me there is no big restriction? Does anyone have any suggestions?
    Mar 2009
    Triad - North Carolina
    System Age? R22? Have you checked the outdoor metering device if heat pump? Reversing valve in midshift / stuck?
    Yes, I've seen that before and it doesn't mean I like it.
    Dec 2010
    On a Peninsula in NE NC
    need more info. heat or cool when it does this? what do you mean when you blow the system the pressures elevate? are you sexually harassing this ruud?
    Jul 2010
    So-Cal
    Quote Originally Posted by Southern Mech View Post
    Jan 2011
    minnesota
    have had problems from not dble checking txv's for heat pumps & find out ac only was sent by whslr & insalled. they work good until heating time comes!
    Dec 2010
    Palm Beach,Fl.
    Straight cool? TXV? Heat Pump? New system or old?
    Jun 2010
    rio grande valley
    Quote Originally Posted by SoFlaDave View Post
    older model Ruud 10 seer, cap tubes straight cool, not heat pump, the suction line does have some semi flattened curves but the pressure does flow through quickly. This systems evp coil was recently takened out and washed.
    Dec 2010
    New indoor coil needed
    Dec 2010
    Palm Beach,Fl.
    Sounds like plugged cap tubes. Even if you can get nitrogen to flow through there, refrigerant and oil is much denser than nitrogen. What Southern Mech said.
    unplug the supply fan!
    where it ices up is where your restriction is!
    true knowledge exists in knowing that you know nothing.
    Houston,Tx.
    If it's a scroll, the compressor is running backwards, swap your two 120's at the contactor and your good to go.
    Dec 2010
    Palm Beach,Fl.
    You're not serious. Right?
    Dec 2010
    what? I know what you are saying but, what?