    Quote Originally Posted by sprangdog View Post
    Do they make a smaller-profile transformer that I could maybe rig up inside the unit? Now I have a typical bell-type which is way too bulky to get inside.
    Now I am worrying that you may end up using an undersized transformer.
    Quote Originally Posted by sprangdog View Post
    I just assumed a high voltage relay would still work with lower-than-rated voltage. It will burn up too?
    Yes.

    These kind of questions is why you need to bring in a professional. This is a relatively simple thing to do; however, the assumptions you have made and your attempts are all leading to likely burning up a transformer, actuator and possibly more. If space limitations are such then one could mount the transformer in an external j-box and pull wire, or better yet get an actuator that is rated at 120VAC and get rid of the transformer. If your fan is so oversized I would look at putting an external switch anyway just to open the damper so you don't have to run the fan just to cook something little. *Just realized downdraft, so no fan then draft will likely go the wrong way, but* Then one could interlock an end switch and.....bring in a professional.

    We don't want a conversation such as:
    your insurance agent "Well it seems the electrical in your kitchen ventilator caused the house fire and since it wasn't inspected/proof that it was professionally wired your insurance policy is null and void on the damages caused.."
    You to your agent "Well I learned how to do this on the internet at HVAC-Talk and CM, ...told me how!"

    Good luck to you and you might post your general location, who knows maybe one of us lives near you/knows someone that does.
    Last edited by crab master; 01-04-2011 at 10:33 AM. Reason: **
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    http://threedevilskennel.com/ - not my website.
    Versatile Hunting Dog Federation - www.vhdf.org/


  2. #15
    Thanks for talking through this, still not sure exactly what I will do, but I have a few ideas and maybe the current sensing relay is something I'll look into. Don't worry I won't do anything based on assumptions, I do want to respect the no DIY policy here, so the bottom-line is that you guys think the 24v actuator can be damaged by under-powering it. Thanks again for the help.

  3. #16
    Join Date
    Sep 2007
    Location
    SoCal
    Posts
    135
    Yo Dog, most guys (or gals) on this site would probably love to help engineer a solution for you but the variables are too vast to give responsible advice over a bulletin board and still feel comfortable that you will not light yourself up.
    Having said that, the fact that the actuator motor only opens partially tells me that at 16v the motor does not have the torque to overcome the return spring. So I think that would eventually lead to the demise of the actuator motor. Without knowing how far "point A" is from "point B" its hard to say what the best way to do something would be.

    My email is in my profile.
    Best of luck.

  4. #17
    Thanks again. I've ordered a low-voltage current-sensing relay (the kind typ used for humidifiers) and will wire the power to the transformer on the primary feed. This will keep the solution on the 24v side. AS a side issue I love the outdoor blower/ventilator setup but it really surprises me that these systems don't integrate a damper... I know that homes can be a little too tight these days but an open 8" round duct from the kitchen to the outside isn't getting it in my (midwest) book.

Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event