Results 1 to 5 of 5
  1. #1
    Join Date
    Feb 2005
    Posts
    39
    Post Likes
    I checked the builder's Manual J and I'm concerned about it having no heat gain from the exposed basement walls. The wall is 53 ft, faces the west, is brick and has four windows and a french door. Also they have no heat gain for two 30 feet north and south walls where they start above ground and end below ground.
    They do have 3,100 gain for the basement and added latent gain of 4,500 for 7,600 total basement heat gain for our walkout basement. Also they have no loss for ductwork.
    Does this sound correct?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    73,359
    Post Likes
    If the duct work is in a conditioned space, then the is no gain for it.
    So then is your east wall totally under ground?
    Sort of cancels most of the gain from the west wall.

    Do your self a favor, and click the bulls eye, and do your own load calc.
    Then you can compare it to the one your builder did and ask him and his hvac contractor about any differences there might be.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Post Likes
    What percentage of the N and S walls are aboveground?

  4. #4
    Join Date
    Feb 2005
    Posts
    39
    Post Likes
    About 50% of the north and south wall are underground. They go from the corners of the long west wall above ground and finally go to 100% under ground on the corners of the east wall. The east wall is totally underground.

    Question: can you explain the grain from the first reply. I know very littly about HVAC.
    Thanks

  5. #5
    Join Date
    Jan 2005
    Location
    Seattle
    Posts
    191
    Post Likes

    Wink grain

    help3. If you what you ment to say was. What do the first response mean by gain (not grain)the anwser is there is not any heat gain (or loss) from the ducting because the ducting is IN the conditioned space.Hope we can help you more.
    41Gasman

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365