Page 2 of 2 FirstFirst 12
Results 14 to 17 of 17
  1. #14
    Join Date
    Mar 2003
    Posts
    7,253
    in essence, it is the pressure drop through the longest EQUIVALENT circuit. this can be the physical longest, or the one with a lot of restriction. thee is a formula to size the pump using this information to tell you if that little 007 is right or not.

  2. #15
    Join Date
    May 2010
    Location
    SF Bay Area, CA
    Posts
    390
    Are all 17 loops controlled by one thermostat or are there multiple zones and zone valves?

    As others have said, there's probably both a pump size issue as well as a balancing issue between all of the circuits you have.

  3. #16
    Join Date
    Jul 2010
    Location
    Scarborough/Toronto, Ontario
    Posts
    8
    Drewski11, we have one thermostat. There are valves on each of the four tubes running off of the _radiant-floor manifold_. There was a differential controller for pump on the radiant-floor loop, but we removed it because we are not using the solar system as a heat source. The radiant-floor loop pump now runs all the time.
    If I can figure out how to upload pictures, I'll try to do so.

  4. #17
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,139
    Mother, it is impossible to offer specific advice on something we can't see. seems that you are interested enough to seek some preliminary advice you'll now seek out someone who can try to document what you have installed to first understand BEFORE they can offer intelligent solutions and not best guesses or opinions.
    Your original permit info on file with the Municipality for instance. You can check on that but if not available then some educated guesses might be in order,
    Happy New Year
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •