Results 1 to 13 of 17
Thread: Variable speed blowers
-
02-11-2005, 09:36 AM #1
Can anyone tell me where I can get info on why's of using a variable speed blower to obtain higher eff.
I can understand varying the blower speed if you vary the compressor speed also. In other words, varying the blower speed as the load on the house decreases and your system output decreases.
What i can't seem to grasp is changing the blower speed without changing the unit output load.
My big problem is that when you lower speed, the system runs longer. I can see where comfort could be better, but what about energy eff. if the system runs longer, even at a lower amp draw.
-
02-11-2005, 09:38 AM #2
ECMs use much less juice than their PSC counterparts. Anything that uses less juice in a system raises the SEER and HSPF. Those ratings figure in what wattage a blower motor uses, usually estimating but if you see a rating with a matching furnace or air handler, the exact wattage was used.
-
02-11-2005, 09:46 AM #3
Your required elctricty input is less with the same cooling output. Thats efficiency. The other features of VS such as dehumidifying properties are all comfort related.
You cannot confuse comfort and efficiency, they are not the same but the better system considers both.
-
02-11-2005, 09:57 AM #4
-
02-11-2005, 11:55 AM #5
Professional Member
- Join Date
- Nov 2003
- Posts
- 257
The purpose of the lower speeds is to improve comfort. Most systems with variable speed blowers aren't run at the lower speeds for more than a few minutes unless there is a need for extra dehumidification. The lower speeds at startup help to get the indoor coil to temperature sooner than with a standard PSC blower. This helps promote better humidity removal in cooling and less cold-blow in heating. An unfortunate side effect of increasing the efficiency in cooling mode has been a decrease in humidity removal capability, the use of ECM motors has allowed manufacturers to combat this problem.
-
02-11-2005, 11:59 AM #6
Regular Guest
- Join Date
- Jan 2003
- Posts
- 88
Running longer (and lower) in the summer means more dehumidification (especially when you're not at the limits of the system). More dehumidification means more comfort, or the same comfort at a higher temp. Same comfort at a higher temp means less expense to be comfortable (and they don't take that part of it into consideration, they assume same temps when calculating efficiency). Also better mixing (more even temps), less noise, smoother start/stop, etc - most of which (other then more even temps) don't affect efficiency.
-
02-11-2005, 03:39 PM #7Perhaps re-thinking your term "unit output load" might clarify the matter for you. If you are thinking in terms of what emerges from the supply registers in relation to blower speed, this isn't where you want to look. The true load is from the return air passing over the evaporator coil. If you slow the blower speed without reducing compressor capacity, the coil will run at a colder temperature and will result in colder air emerging from the supply registers.What i can't seem to grasp is changing the blower speed without changing the unit output load.
However, let's say the heat load and humidity levels are constant in the space being conditioned, and the outdoor ambient conditions are constant. First we fire up the system on high blower speed. After the system stabilizes, it will reduce both the sensible and latent heat of the conditioned space. The ratio of sensible to latent heat reduction will favor sensible heat due to maximum airflow over coil at rated BTU of coil and condenser.
Now, same system, same conditions, but reduced blower speed. The system will now reduce both sensible and latent heat as before, but the ratio tips toward latent heat removal over sensible.
Overall, the system will run at shorter intervals under high speed conditions because the sensible heat reduction is faster, leading to faster thermostat satisfaction. Longer intervals will be the case with reduced blower speeds due to slower sensible heat reduction to satisfy the thermostat.
Ideally, for best efficiency, the system would be able to operate a blower at higher speeds for higher sensible/lower latent loads and operate at lower speeds for higher latent/lower sensible loads. The reduced blower speed (with ECM) and reduced outdoor ambient (resulting in lower compressor head pressure) will offset the longer run times to accomplish dehumidification and space temperature reduction."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
02-11-2005, 05:24 PM #8
Thanks for response:
Shophound,
Thanks for very good explanation. Further questions please as I have never had to deal with ecm motors.
What factor determines the speed of the motor - what factors involved?
Also are the ecm motors variable over the entire range ( from 0 to full speed ) or are they more like a two or three speed motor?
And yes, I was concerned about the coil freezing if the blower speed got too low, if the refrigeration wasn't reduced.
[Edited by bornriding on 02-11-2005 at 05:27 PM]
-
02-11-2005, 05:51 PM #9
before you get overly excited about 2 stage cooling dehumidfying better you need to look at the latent work being done during that time frame. The latant capacity during the low stage is generally not as rewarding as you may think. Just because its running longer doesnt truely mean its going to dehumidify better.
Maybe someone who has data can share thier findings.
-
02-11-2005, 05:57 PM #10
The ECM's are designed for a specific unit, the software determines the flow rates. Generally in a furnace you would have several cfm settings.
Fan on -(about 1/2 nominal cfm if selected)
Heat - faster than fan only (proper for furnace design)
Cool - Fastest select
10% increase
10% decrease
15 percent decrease (dehumidify).
ECM's can be programmed to run at any speed the programmer wants but generally he has protection built in depending on the unit. They can also be programmed to be a single speed motor. Best thing is to read the configurations for each peice of equipment and be sure not to use a module not configured for the unit in question.
-
02-11-2005, 06:12 PM #11
Re: Thanks for response:
On residential applications I am still on the learning curve in regard to variable speed blowers, but my understanding is that static pressure most often determines ECM motor speed. The electronic equipment monitors the torque and speed of the motor, which is affected by the static pressure of the equipment and ductwork.Originally posted by bornriding
Shophound,
Thanks for very good explanation. Further questions please as I have never had to deal with ecm motors.
What factor determines the speed of the motor - what factors involved?
Also are the ecm motors variable over the entire range ( from 0 to full speed ) or are they more like a two or three speed motor?
And yes, I was concerned about the coil freezing if the blower speed got too low, if the refrigeration wasn't reduced.
[Edited by bornriding on 02-11-2005 at 05:27 PM]
On the commercial equipment I'm familiar with, the blower motor is an AC motor regulated by a frequency drive. Depending on application, it is often regulated by a static pressure sensor in VAV applications.
Variable speed motors are likely variable through the entire range, but for residential HVAC applications, the full range isn't needed.
The coil would freeze under reduced airflow conditions if the capacity was not reduced either by superheat regulation (TXV) or staging the compressor, or both. If the equipment is sized correctly for the house, long run times, which normally lead to a freeze-over of the coil under reduced airflow conditions, would not be a significant factor. A TXV would regulate superheat to prevent liquid floodback to the compressor."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
02-11-2005, 07:08 PM #12
VS drives
Shop,
I, like you, are familiar with the commercial / industrial concepts of blower speed control ( freq. drive)
but as you said, this control is based on "load conditions" when the system has various zones.
I just wasn't sure what was being accomplished ( other than the manuf. getting a better seer rating ) by variable blower speeds on a residential, one stage cooling system.
And Doc,
When you say 'not to use a module not configured for the
unit', I'm not sure what the 'module'is. I assume ( that word again ) that the module is the electronic board that controls the motor, and that the board and the motor go together. So do not put just any 'board' with any ECM. Or do you mean the entire evaporator unit ??
Is not the 'module' a frequency drive system, and what makes the ECM motor special??
-
02-11-2005, 07:47 PM #13
Born,
Check out this link for ECM motor info:
http://www.geindustrial.com/cwc/prod...ecm&lang=en_US"In this house we obey the laws of thermodynamics!"
- Homer Simpson


Reply With Quote