Results 1 to 3 of 3
-
03-07-2005, 04:25 PM #1
Regular Guest
- Join Date
- May 2004
- Posts
- 175
For a 2.5 Ton ADP heat/cool AHU, how could I matchup to a Goodman CLK 13SEER Condenser effectively? The Goodman evaporator for this condenser is a larger (3.5ton) A coil, while the ADP lists a smaller slant coil (2.5Ton).
No ARI match for Goodman and ADP that I know of but would like to at least get 13SEER.
-
03-07-2005, 05:59 PM #2
I'd give ADP a ringy-ding. May be able to compute something for you since 3rd party coil ratings are computer simulated. 1-800-848-2270
Anything without a ratings is a WAG. My WAG would be take a 3 ton AH and put a TXV kit on it. Probably do better than the big piston Goodman coil.
-
03-08-2005, 08:16 PM #3
Regular Guest
- Join Date
- May 2004
- Posts
- 175
Loonie,
Called ADP Tech. They do have some matchups for Goodman. For the 2.5Ton AHU they had a matching unit for the Goodman CLQ (14SEER unit) which should work for the CLT. In fact I have a suspicion that the CLT is the same condenser as the CLQ and Goodman upsizes the coil to achieve 14SEER. TXV comes factory installed on the coil from ADP.


Reply With Quote