Results 1 to 7 of 7
-
01-02-2011, 09:05 AM #1
Regular Guest
- Join Date
- May 2007
- Posts
- 20
Low water PSI on oil fired hot water furnace
Is it normal for the water pressure gauge to only read 0-5 PSI? When the furnace turns off at ~ 180F, the water pressure is about 4-5PSI. There's considerable amount of water deposits coming out from the expansion tank safety valve and a lot of gurgling in the baseboards. Based on my experience when I had a hot water furnace the gauge should always read 10-15PSI. Not looking to DIY, just determining if this is normal and, if not, how long I should wait to call a service tech. Thanks in advance.
-
01-02-2011, 09:13 AM #2
Sounds like you have multiple problems. The relief should not be weeping and needs to be replaced and the fill valve is obviously not functioning either.
You need to place a service call right away
There is generally no low water protection installed on a residential boiler and running them dry can result in some really, really, really bad things happening
-
01-02-2011, 10:27 AM #3
Regular Guest
- Join Date
- May 2007
- Posts
- 20
-
01-02-2011, 10:29 AM #4
-
01-02-2011, 11:48 AM #5
Professional Member
- Join Date
- Jan 2002
- Posts
- 1,196
And Mike: it's a boiler. Not a furnace
-
01-02-2011, 05:26 PM #6
Regular Guest
- Join Date
- Jan 2010
- Location
- Athens GA
- Posts
- 1,234
You really do have multible problems and do have a dangerous situation.You need service right away.
While they are there,residential low water cut off is fairly cheap and easy to install.If I were you I would also have a spirovent installed These are a couple of things that could be reused on a new boilwer if that is the way you go and well worth the cost.
-
01-03-2011, 10:16 PM #7
Regular Guest
- Join Date
- May 2007
- Posts
- 20
hydronicsman: you're right - I stand corrected

I advised my father in law to call a service rep and sure enough the relief on the expansion tank was bad along with the backflow valve. Unit was low on water but after repair pressure ranges from 15-20PSI on/off. I knew something didn't sound right that morning....
Thanks again.


Reply With Quote