    Hello guys.
    Why would you have a solenoid valve installed in liquid line about 20" away from evaporator(metering device) in a regular air conditioner?

  2. #2
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Thats where it belongs. Ok nothing says 20" but it belongs inside by the indoor coil when it is used.

  3. #3
    Join Date
    Jul 2004
    Location
    NJ
    Posts
    56
    Post Likes
    Thread Starter
    Thank you for the response Docholiday. BTW my favorite charecter in tomb stone. EXCELLENT.

    BUT, why is the solenoid valve there? no need for it. correct?

  4. #4
    Join Date
    May 2004
    Location
    new jersey
    Posts
    338
    Post Likes
    does the unit have a low pressure cut out?
    if so it's for automatic pumpdown, solinoid closes causing unit to go off on low pressure.when the compressor calls again there's not a big load on it.

  5. #5
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    carrier is the only equip i have seen this regularly done.
    i do not think it pumps down, valve stops refrig migration when unit is off.

  6. #6
    Join Date
    May 2004
    Location
    new jersey
    Posts
    338
    Post Likes
    my mistake,
    the only time i've seen liquid line solinoids is on commercial splits,and they where for pumpdown.

  7. #7
    Join Date
    Aug 2003
    Posts
    47
    Post Likes
    Magic Chef, (Armstrong) did this in mid 1980's. 8 seer
    a/c units. Could add selenoid valve near evaporator coil,
    paralell with low voltage to condenser. When condenser stopped at end of cooling cycle, selenoid closed, trapping liquid line full of liquid refrigerant. Also required adding start assist kit on compressor. Next time on call for cooling, the refrigerant was there @ evaporator coil, ready to begin cooling cycle. They claimed this would raise seer to "9"

  8. #8
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    Does the condensing unit possibly have a scroll compressor? First generation scrolls required a solenoid valve to stop reverse rotation of the scroll when the thermostat cycled off. If you ever replace a scroll that has a solenoid you'll need to remove it as the new compressors do not require a solenoid valve.

  9. #9
    Join Date
    Mar 2005
    Posts
    39
    Post Likes
    docholiday was my favorite character in Gunsmoke.


Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •