    Outdoor Sensor

    I have a Lennox system that was installed two years ago that has never seemed to be function as it should. The system consists of a heat pump with propane back up, but the propane runs 90% of the time even when temps are in the mid 50's. I suspect the outdoor sensor to be the problem, but am curious as to whether anyone has experienced similar difficulty.

    Overall, I am happy with the Lennox quality, but seems like they totally blew it on the outdoor sensor. It is often inaccurate in excess of 30 degrees, so there is no way it is capable of detecting when the HP or propane should be running. I have disabled the outdoor sensor presently and it is much better and the HP has been doing a fine job of satisfying the stat.

    Has Lennox improved on the outdoor sensor?

  2. #2
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    If it never seemed to function as it should, did you call the installing co. and have them diagnose the problem?

    Have not noticed any pattern of failure on their sensors.

    Could be the sensor, connections, wiring, stat, location, etc...........

    Too many possibilities to try and diagnose it from a computer.

  3. #3
    Join Date
    May 2008
    Posts
    45
    Post Likes
    Thread Starter
    Installer is clueless. I had to show him that I could get the HP to kick on. He automatically assumes it is a bad stat. He has replaced the stat on our upstairs unit at least 3X's when I know that something is causing the stat to fail. They are not all bad out of the box.

  4. #4
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Time to call a different contractor.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Is the outdoor sensor mounted on the North side of the house, or elsewhere.

  6. #6
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,976
    Post Likes
    The outdoor sensor wire needs to be run in a separate cable from the thermostat cable or it will not read right all the time.
    Remember, Air Conditioning begins with AIR.

  7. #7
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    location. It's probably above the outdoor unit.
    "The only true wisdom is in knowing you know nothing" Socrates

  8. #8
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    477
    Post Likes
    Where is the sensor, exactly?
    ENJOY THE RIDE

  9. #9
    Join Date
    Dec 2010
    Location
    Wisconsin
    Posts
    22
    Post Likes
    You might want to listen to Chuck and find you a different contractor. Sounds like you know about as much or more than the tech that has been servicing your system. It probably has something to do with the location of the sensor, as others have noted.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •