    OK iam going to school for hvac and was having a discussion the other day

    with a guy in the same class hes working now installing residential heat pumps

    here in Iowa and hes having a problem charging the heat pumps he say that if there

    is too much air flow across the inside coil in heat pump mode that it will cause system to kick out on high head

    now that would mean that too much air across the condenser would cause high head ?

    does not make sense to me

    he and my teacher argued that the air moving across the coil would not have enough time to pick up any heat thous causing the coil to get hotter not cooler this does not

    jive with any books i have read and i have reed allot . iam probably the only one in

    class teacher included that has read the whole book

    Evey thing i have read says that more air flow = more delta T = more heat pick up / rejected i say that more air flow at a faster rate will mean that each

    cubic foot of air will have less delta T but there will be more per min

    witch will mean that more heat/ BTU removed = lower temp = lower head

    and i say that once you reach a certain amount of air you will reach the max amount of BTU

    that can be removed from the coil with out an ambient air temp change

    even if you are able to push more air through that coil .

    is what they are saying right or wrong

    if they are right please explain or point to to the place to find the explanation

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,311
    Take a heck of a lot of excess air flow to do it. Guessing you would probably need over 700 CFM per ton to do it.

    Many manufacturers want 450 CFM per ton in heat mode.

    How much air per ton does this guy say these units had moving through the coil?
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Oct 2005
    Location
    phoenix az
    Posts
    429
    Quote Originally Posted by johnwas64317 View Post
    OK iam going to school for hvac and was having a discussion the other day

    Evey thing i have read says that more air flow = more delta T = more heat pick up / rejected i say that more air flow at a faster rate will mean that each

    cubic foot of air will have less delta T but there will be more per min

    witch will mean that more heat/ BTU removed = lower temp = lower head


    if they are right please explain or point to to the place to find the explanation

    The faster the air moves across the coil the less heat that it picks up. The less heat that it picks up the more heat that stays in the coil. the more heat that stays in the coil the higher the pressure.
    "Do not let what you can't do interfere with what you can do"

    "Do what you can do the best that it can be done and no one will ever know what you can't do"

  4. #4
    Join Date
    Dec 2010
    Location
    Northern Virginia
    Posts
    55

    Heat Transfer

    Well, you say you like to read? Here are some documents related to the subject.
    Attached Images Attached Images
    Attached Files Attached Files
    Π r2----No, pie are round, cornbread are squared.

  5. #5
    Join Date
    Jun 2010
    Location
    Western Nebraska
    Posts
    246
    Are these installs on dual-fuel systems with the indoor coil sitting on top of a running furnace in second stage? Maybe he is missing a jumper or a solder trace that needs to be cut upon install, and the furnace is kicking on while he is commisioning the heat pump? Would like to know what you find out.

  6. #6
    Join Date
    Apr 2002
    Location
    Omaha, NE
    Posts
    1,561
    Quote Originally Posted by johnwas64317 View Post
    .........snip........................
    cubic foot of air will have less delta T but there will be more per min
    witch will mean that more heat/ BTU removed = lower temp = lower head
    and i say that once you reach a certain amount of air you will reach the max amount of BTU
    that can be removed from the coil with out an ambient air temp change
    even if you are able to push more air through that coil .
    is what they are saying right or wrong
    if they are right please explain or point to to the place to find the explanation
    It's my opinion that you are right and they are wrong. The more air thru the condenser the more total heat will be rejected. As the Delta T is reduced, the slope of the heat rejection will lessen, but it will still reject more total heat.
    See the Florida Solar Energy document that Lambo posted. Look at pg. 6 Fig. 4. That graph tells the story.

    http://www.fsec.ucf.edu/en/publicati...CR-1674-05.pdf
    B.O. = B.S.

  7. #7
    Join Date
    Dec 2010
    Location
    Northern Virginia
    Posts
    55

    Show me in writing.

    I'm with you Snewman----for now----unless someone can prove otherwise. I was also told by one of my superiors, years ago, that this could happen. In fact, we had one rooftop condenser that we thought had this issue. We had four techs up there making sure that a previous company had not replaced the motor with one having the wrong RPM, or a blade with the wrong pitch, etc. This was all after cleaning coils and evac/recharge to exclude non-condensable----bla--bla--bla. I can't recall what the outcome was, but it wasn't an excessive air quantity/velocity issue.
    I do know that this can apply to water through a chiller barrel, but I can't find any published proof that it can apply to air across a fin-tube coil. I know that we have several "phenomena" to deal with in this trade. They all have an explanation based on physics, thermodynamics, or some other field of science, yet somehow seem to defy initial logic. I actually want to believe that it could be true---but can't find proof.
    Π r2----No, pie are round, cornbread are squared.

  8. #8
    thanks to lambo and snewman24 for the papers
    they confirm what is said there problem of kicking out on high

    head is not caused by too much air flow across the condenser coil
    i agree with you lambo that it might be possible but can not find
    proof so i will make proof i will prove one way or the other
    form my class project and will post the results here .
    in about 8 weeks ( thats when project is due )

    but something else not sure what there problem is as i believe they are doing

    more than one thing wrong and iam unsure what they are doing

    here's what i know of there problems

    they are installing in existing home with duct work designed for a split system

    natural gas furnace's 80-95 % 's and standard central a/c systems though one i know

    did not have a/c originally in stalled they have installed at last count 28 systems

    like this

    goodman air heat pump / and a couple geothermal

    with gas furnace back-up

    he claims goodman sends this heat pump without an accumulator

    teacher said he was full of s**t that all heat pumps need accumulators

    i agree that heat pump do need accumulators ( this is not from experience but from what

    i have read on heat pump theory and the few i have seen apx dozen so far )

    all systems are being installed with communication thermostats ( there the kicker

    they say that the stat will automatically know what kind of systems - the btu and airflow

    setting need to be without programing or without changing any of the jumper settings on the air handlers )

    i think they are wrong about that .

    and they claim that the system only need about half of the recommended refrigerant

    that the specs call for .and usually the systems are shipped over charged .



    if this is the kind of quality that is in the field now i shutter to think .

    this is the kind of **** i saw on my job shadow where the top service

    tech took 4 hrs to change a heat pump relay for back up electric heat

    and did not get it hooked up correctly let the system not working

    and no he would not here any thing i said he had the 20 years experience

    and i was to stand there and shut up .

    ( that was a different company than this other student is working for )

  9. #9
    Join Date
    Nov 2009
    Location
    Saskatchewan
    Posts
    492
    DO not worry to much about what your being taught.

    Because: A great mind will always over come BAD teachings.

  10. #10
    Join Date
    Apr 2002
    Location
    Omaha, NE
    Posts
    1,561
    [QUOTE=johnwas64317;8881811s............ .snip............................

    he claims goodman sends this heat pump without an accumulator

    teacher said he was full of s**t that all heat pumps need accumulators

    i agree that heat pump do need accumulators ( this is not from experience but from what

    i have read on heat pump theory and the few i have seen apx dozen so far )

    [/QUOTE]

    You need to read these threads (& others) about whether heat pumps always have accumulators:

    http://hvac-talk.com/vbb/showthread.php?t=532152
    http://hvac-talk.com/vbb/showthread.php?t=226012
    http://hvac-talk.com/vbb/showthread.php?t=150928
    B.O. = B.S.

  11. #11
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,311
    As above. Not all heat pumps have accumilators.

    Some where down the road, you run into some that have charge compensators.

    In school, you will be taught what a heat pump can, and can't do. In the field, you will learn a heat pump can do everything school told you it can't do.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    kenney t Guest
    Quote Originally Posted by deux View Post
    DO not worry to much about what your being taught.

    Because: A great mind will always over come BAD teachings.


  13. #13
    Join Date
    Dec 2010
    Location
    Northern Virginia
    Posts
    55

    Refrigerant charge compensators

    Attached are some examples of refrigerant charge compensators. The one example shows the use of the compensator in combination with an accumulator. There are probably designs out there that use only the compensator, but I would imagine that they would only be in combination with the more slugging tolerant scroll compressors. Still looking for other info.
    Attached Images Attached Images
    Π r2----No, pie are round, cornbread are squared.