What causes a Metasys ASC device {VAV,UNT etc} to cycle online offline and report as "INCOMPATABLE" in the Metasys critical alarm summary?
Thanks,
Mark
-
03-05-2005, 01:46 PM #2
Regular Guest
- Join Date
- Oct 2004
- Posts
- 875
More info please...
Existing device or newly added to N2?
What type of device?
Which supervisory controller and what version?
-
03-05-2005, 04:07 PM #3
Professional Member
- Join Date
- Mar 2005
- Posts
- 11
An existing Metasys UNT controller would not stay online. I replaced the UNT with the same. New UNT 111-1 did the same thing but also indicated "INCOMPATABLE" when offline in Metasys.
I am running PMI 12.04. The old and new UNT was addressed 100. I just changed the N2 address to 98 and it seems to be staying online. Not sure what caused this.
-
03-07-2005, 01:33 PM #4
Professional Member
- Join Date
- Mar 2005
- Posts
- 11
Thanks everyone I'm all set with this problem. I changed the N2 address and the UNT hasn't cycled offline yet.