    What causes a Metasys ASC device {VAV,UNT etc} to cycle online offline and report as "INCOMPATABLE" in the Metasys critical alarm summary?

    Thanks,
    Mark

  2. #2
    Join Date
    Oct 2004
    Posts
    875
    More info please...

    Existing device or newly added to N2?
    What type of device?
    Which supervisory controller and what version?

  3. #3
    Join Date
    Mar 2005
    Posts
    11
    An existing Metasys UNT controller would not stay online. I replaced the UNT with the same. New UNT 111-1 did the same thing but also indicated "INCOMPATABLE" when offline in Metasys.
    I am running PMI 12.04. The old and new UNT was addressed 100. I just changed the N2 address to 98 and it seems to be staying online. Not sure what caused this.


  4. #4
    Join Date
    Mar 2005
    Posts
    11
    Thanks everyone I'm all set with this problem. I changed the N2 address and the UNT hasn't cycled offline yet.