    Can anyone explain why the small un-insulated freon line, going from the coil in my oil furnace to the compressor unit outside, is dripping wet with condensation? The water is dripping onto my drop ceiling creating stains. What can I do to fix this? Is there a problem with the system?
    Thanks in advance,
    Jeff
    Maine
    The smaller uninsulated line is the liquid line, if it's sweating that means the liquid is boiling off in that line, undercharged probably, could be low head pressure due failing comp? Call for service and have someone check it out, and make sure they charge by superheat or subcooling, which method depends on the type of metering device.
    Nov 2002
    emerald city, sc
    is this happening with the unit running in cooling mode, the heating mode, or off.
    i wanted to put a picture here
    Nov 2003
    This is happening while running in the heating mode in the winter MD climate.
    Jan 2002
    Ft.Worth,Tx
    Need to have unit checked by professional. But, for now try and get some insulation 3/8" and cover the line from evaporator to where it goes through the wall.
    'Life begins with the journey each day'
    Nov 2002
    emerald city, sc
    insulating the pipe will be the cheapest fix
    midwest
    Jeff, I am very interested in your problem if its anything like whats happening with a couple of our units. Is your unit a A/C only and not a heat pump? When this drips, is the outside unit off?
    Feb 2005
    Dothan, Al
    Jeff
    Is the coil for the oil furnace in the attic with the lines.
    In other words, is the cooling coil above the refrigerant lines. Or do they go up from a closet type furnace & coil, into the attic ( or overhead space ) ?
    Nov 2003
    I believe the unit outside is a/c only and has been off since the end of summer. The A-coil in the furnace is in the basement below the freon lines. I can insulate the line, however, will that only cover up a real problem?
    midwest
    Is this a new A/C unit and is the furnace in a basement?
    Nov 2002
    emerald city, sc
    there is no real problem. the condensation is coming from the migration of refrigerant caused by the changing temp of the evaporator coil. other than insulating the line, the only other option is installing a solonoid valve on the liquid line. when your furnace runs it acts like the flame on an absorption system.
    Feb 2005
    Dothan, Al
    Jeff
    Yes, insulating lines is just temporary cover-up to possibly save ceiling until proper repair is made. At least that what I took it to be.
    You have puzzling problem. I'm sure many are trying to help solve it.
    Does the return air being drawn into your system going through the cooling coil first and then the funace, or is the air going through the furnace before it goes through the cooling coil ??
    midwest
    Can you explain why I have two systems exactly the same and only one is doing this? So far the factory techs can't tell me what is causing this.