    Question Carrier Inifinity Furnace and Thermostat/Controller Operation

    I live in Arlington, Texas and just had a Infinity 80 furnace (Model 58CVA110) installed on December 3, 2010. I kept my old coils and outdoor condenser unit. I do have the Carrier Infinity thermostat.

    Since the furnace has been installed, it's within easy earshot in the garage and it seems the only speed the thermostat chooses is high speed. I understand I can dictate the fan speed by choice, but I wondered, in some circumstances, if the variable speed should be chosen by the thermostat. Or is that only for complete systems which have the Infinity coils and condenser (which also makes the outdoor thermometer reading available)?

    Also, with this setup, am I getting any value out of the two-stage heat for efficiency?

    Finally, does anyone know if the Inifinity Termostat/Controller has any feature which would display how long the unit has run over a period of time which could be reset (say on the day of my meter reading each month). That seems like it would be an extremely easy thing for Carrier to provide in such an intricate Thermostat as the Infinity's. Anyone know by chance?

    Tom
    tomwilson64@hotmail.com

  2. #2
    Join Date
    Apr 2009
    Location
    Central New Jersey
    Posts
    253
    Tom,

    Your furnace should run in both low and high stages. You can verify this with the status screen by pressing the lower right hand button for three seconds. It will display the fan speed and the staging of the furnace. I would expect the furnace to be in the low stage when the thermostat is trying to maintain a temperature set point. If it never goes into low stage, then call your contractor. Something may be wrong with the installation.

    There is a run time indicator in the service menu section. You have to hold down the advanced button for 10 seconds to gain access to this menu. Once you are in, select Service, then Run Fault History, then Run Times. You will see display of the number of lifetime hours for the various furnace stages. I don't think you can reset these values. You will have to keep your own history in order to calculate the monthy usage.

  3. #3

    Frown

    The two-stage may be working. I'm also wondering though about the variable speed. The blower sound seems to remain consistently on the high speed. I know how to force it to low or medium speeds, but I don't know if the Infinity, with the furnace only installed, will automatically adjust the fan speed or not. I know this would only save a very small amount on the electricity the blower is consuming, but wasn't sure if anyone happens to know the answer to this additional question.

    Thanks!

  4. #4
    Join Date
    Dec 2010
    Location
    Saskatoon, Saskatchewan
    Posts
    7
    Check your filter, on any Infinity furnace (or most variable speed furnaces for that matter) the variable speed fan will ramp up its rpm to try to maintain whatever airflow it wants. If your filter is plugged, the fan may reach 100% rpm just to achieve low speed airflow. There are dip switches on the board to control the amount of airflow the furnace will provide on continuous fan and air conditioning but the low and high fire speeds are predetermined by Carrier and can only be adjusted 15% or so. These dip switches are there only for installations with a traditional 24 v thermostat and are ignored by the furnace once the Infinity control is connected, theair flow settings must be adjusted from the infinity thermostat itself.

  5. #5
    First, thanks so much for all replies. My new Infinity furnace was installed December 3, 2010 with a 4-inch filter. So I can easily check the filter and will, but having only had the furnace for 25 days with a 4-inch filter it shouldn't normally be the filter I wouldn't think.

    Also, something unusual is that the Infinity THermostat displayed a need for me to change the filter a few days ago, exactly three weeks after installation. Should it show that soon?

  6. #6
    Join Date
    Dec 2010
    Location
    Saskatoon, Saskatchewan
    Posts
    7
    Typically a 4" filter should last alot longer than 25 days. That being said, if you didn't have your ducting cleaned prior to the install, the higher airflow rate of the new furnace can pull a ton of dust balls into the filter and plug it within minutes. That would be a rather extreme case of dirty duct work though.
    Check your filter first, and then call your installing contractor to double check the install. He probably checked his temperature rise and gas pressures at install but with the infinity stat he can also check things like fan rpm at a given cfm and max external static pressure. When the system was first powered up, it would've gone through a series of startup checks one of which is the external static pressure check. As the filter collects dust, the ext static will go up, when it reaches a certain level, the stat will give the filter reminder. This process happens faster if the system has alot of ext static to start with, this could be caused by duct work that is too small (it may have worked ok with the old furnace with a 70-100 degree temp rise, but the new is probably 30-50) or maybe a bunch of the supply air diffusers are closed or restricted.
    Anyway, check the filter, check the registers (return airs too!) and if those fail, call your contractor.

  7. #7
    Join Date
    Dec 2010
    Location
    Saskatoon, Saskatchewan
    Posts
    7
    I live a long way from Texas so I can't say for sure what the best solution is. Up here, in the winter, the outdoor RH drops because the cold air outside can't hold much moisture. Over ventilation of a space would drop the RH just as commerce48 wrote, because you are drawing low RH air from outside and forcing the (usually) high RH air from your living space out through some other leaky hole in the vapour barrier, this could be caused by a leaky building envelope. Sealing your home could help a dry house in these conditions and has the much larger benefit of lowering your heating and cooling costs. There are some fairly simple things you can do to control infiltration like spray foaming around windows and in penetrations through the exterior walls. Realistically however, installation of a humidifier is the quickest, easiest way to address the issue.
    The infinity control has the ability to control humidification and de humidification (either with an HRV or by running the fan at lower speeds while running the condensing unit) The cool thing about the infinty is that it will automatically adjust the RH setpoint based on outdoor ambient temp to prevent high humidity and condensation on windows at low outdoor temps, probably not a real issue in Dallas... The furnace control board has a terminal that supplies 24v (if i remember right...or it might be a dry contact ) to energize a soleniod or run a drum style humidifier and the rest of the controls are already wired from the stat you have.
    You mentioned that you don't have the full infinity system, but you basically do, the furnace and the thermostat are the heart of the system, HRV's, humidifiers, u.v. lights e.a.c.'s are all modular and can be added and integrated into the infinty controls system easily, the hardest one is the HRV because you need to purchase a net work inteface so it'll communicate with the infinity.

  8. #8
    Join Date
    Nov 2009
    Posts
    26
    if your humidity is dropping to 30% and lower you definately want a humidifier, levels that low can cause health issues. as far as choosing a humidifier they are typically sized according to how many gallons of water they can shed to the airstream per day so check with your contractor to recommend the appropriate size. there are also different types of humidifier with different levels of required maintenance. one of the most worry free humidifiers i'm used is a "bypass" type which is installed on the supply duct and warm air from the furnace is forced through the humidifier pad inside and out through a short duct back to the return duct where the humidified air is mixed thoroughly back into the air stream. as for the option on the infinity to humidify with only the fan running and not the heat you should not have an issue with mold or mildew in the duct because the dry air will act like a sponge to absorb the water from the humidifier and there should not be any condensation in the ductwork if the humidifier is properly adjusted.
    also somone mentioned the dip switches on the furnace, when using the infinity control those dip switches are deactivated and all setup is done at the infinity controller
    Attached Images Attached Images  

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event