03-02-2005, 09:22 PM #14Knew I was forgetting something.Originally posted by BaldLoonie
Also, HV systems have BIG blower motors which use more juice & put out more heat. All this is taken into consideration in ratings.
-
03-02-2005, 10:53 PM #15
Professional Member
- Join Date
- Apr 2003
- Location
- the Great Pacific Northwest
- Posts
- 607
Unico:
200 cfm per ton
30 deg delta
30% more latent capacity than conventional
Much larger coils with factory installed TXV's
Follow their rules they don't take well to cheaters.
-
03-02-2005, 11:01 PM #16
Professional Member
- Join Date
- Jan 2003
- Posts
- 948
no dont do it
match conderser with a coil.. It that simple..
regars,
Kelvin
-
03-03-2005, 09:27 AM #17
Regular Guest
- Join Date
- Feb 2005
- Posts
- 10
Thank you all for the information. The unit is matched and working fine.
-
03-04-2005, 02:01 PM #18
Regular Guest
- Join Date
- Feb 2005
- Posts
- 40
Don't know much about Unico, but I have learned over the years, that with the conventional AC split systems,(those that are missed match,larger cond. than coil) you can do best by balancing the system with the Temp. difference across the coil. The gauge readings will not necessarily give you a true reading. I was taught to use the TD across the coil and try to get maxium difference of TD by adding or removing refrigerant,this has worked well with flowraters or metering devices. I have been able to get good performances out of systems that had been mismatched and overcharged by using gauge readings only. Many times, I am sure, some techs don't bother to check the coil size before charging a unit. Most of the mismatched units, I have found on rent houses.The landord wants the cheapest way out and some jackleg will put whatever he has on hand to make some extra money.