    Angry

    Hello,
    I have a two zone system York diamond 90 furnace with Honeywell zone control
    The 1st zone feeds the whole house both floors works ok. the 2nd zone feed one bedroom over the garage 24 sq also works good. But the noise the 2nd zone creates is unbearable a mostly blower noise. is there a way to turn down the blower speed on zone 2 only?

    thanks


  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Sounds like a poor duct design. Is there a bypass installed? Sounds like they skipped that and needs to be done. Can't slow the blower, furnace will overheat worse than it is.

  3. #3
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,849
    Post Likes
    I have to agree with the bald one.
    Karst means cave. So, I search for caves.

  4. #4
    Join Date
    Feb 2005
    Posts
    4
    Post Likes
    Thread Starter

    blower

    there is no bypass
    sounds like i have to get someone down to take a look at it

  5. #5
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    The bald one has spoken.