Results 1 to 8 of 8
  1. #1
    Join Date
    Feb 2005
    Posts
    15
    Post Likes
    what is the diference between a heat pump and your standard condenser?

  2. #2
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,847
    Post Likes
    Expansion device, reversing valve, defrost control
    Karst means cave. So, I search for caves.

  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,780
    Post Likes
    Originally posted by karsthuntr
    Expansion device, reversing valve, defrost control
    Add to that accumulator, fan relay, defrost relay, defrost sensors, high pressure safety switch...

    ...sorry, got carried away.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  4. #4
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,847
    Post Likes
    I was going to add accumulator but couldn't spell it.

    The 10 seer Rheem's do not have the other stuff anymore. All the controls are on the board and they deleted the high pressure saftey on some models.
    Karst means cave. So, I search for caves.

  5. #5
    Join Date
    Feb 2005
    Posts
    15
    Post Likes
    Thread Starter
    Originally posted by shophound
    Originally posted by karsthuntr
    Expansion device, reversing valve, defrost control
    Add to that accumulator, fan relay, defrost relay, defrost sensors, high pressure safety switch...

    ...sorry, got carried away.
    i meant to ask what are the different processes of a heat pump compared to a standard cooling system?

  6. #6
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,847
    Post Likes
    Nothing really, the only thing your doing is reversing the refer flow. The warm air that an a/c blows out in the summer is reversed and blows inside. And because the outside temp is cold you need to add defrost control so the unit doesn't become a solid block of ice.



    This is what I tell HO that ask. It is a very simple explanation and covers most of the bases.

    And if they ask I tell them the unit is picking up heat from the outdoor air and moving it inside the house, and the reverse is true in the summer.
    Karst means cave. So, I search for caves.

  7. #7
    Join Date
    Mar 2003
    Location
    Cincinnati
    Posts
    7,945
    Post Likes
    A heat pump will change the direction of the refrigerant flow. That way insted of taking heat from your house and transferring it outside "like a staight a/c", it will absorb heat from the outdoor air and distribute it into your home.

  8. #8
    Join Date
    Apr 2004
    Posts
    7,676
    Post Likes
    Well I think if you look at the basic concept of airconditioning being "to remove heat from a place where it is unwanted and rejecting it to a place where it is not objectionable" can be reversed when addressing a heat pump to sat remove heat from a place where it is not objectionable and rejecting to a place where it is wanted.

    Bottom line is an air conditioner doesnt produce cool, it moves heat from the evaporator to the condenser. A heat pump moves heat fromm the evaporator to the condenser also, it just switches which coil fills what role.

    You also have to understand that there is no such thing as cold, only heat or a lack there of. Since the total absence of heat is absolute zero (not 0*F or 0*C). Anything above it contains heat, the HP or A/C simply moves it.

    [Edited by docholiday on 02-27-2005 at 12:06 AM]

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.