    Drafty floor returns. Why?

    Cold air drafts up from first floor returns when furnace is off. Located in Massachusetts.

    New furnace and ducts installed in a 2 story house with basement (retrofit). Furnace and ducts are properly sized. Second floor returns are in the ceiling with trunk in the attic. First floor returns are on floor. Trunk runs from attic to basement through a chase located along exterior side of house. In the basement, the first floor returns connect to the return trunk and the trunk the extends to the furnace. All joints are sealed and all connections are tight. All ducts outside of conditioned space are insulated. Basements walls are insulated.

    Do you think warm air rises into the second floor ceiling returns, cools, and travels down the attic trunk return and to the basement? Cool air is heavy. The first floor return, which are connected to the return trunk in the basement, allows the cooled air to enter the first floor. Basically air is circulating through this path.

    Have you heard of this before? How to stop? A damper in the return trunk where it enters the basement would stop airflow when the furnace is off. Motorized dampers are more efficient and costly. Baromatric dampers are passive and cheaper, but they reduce the flowrate through the return (high resistance).

    I installed an attice return because I did not have enough return on the second floor, hence retrofit. The work was expensive and I don't want to reduce the attic return capacity with a barometric damper (if barometric dampers create high resistance.)

    Any thought anyone?

  2. #2
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,086
    Return duct running along an exterior wall...even if insulated it will lose heat faster during the furnace off-cycle...cold air sinks as you say.

    Could be a combination of this and stack effect...if any of that attic duct run leaks air it will let heated air from the house escape into the attic, which must be replaced down low by colder air.

    Does this system have a fresh air intake from outdoors? That could also allow cold air to draft in from outdoors.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event