    Could someone help me explain the difference between none-bleeding expansion valve and bleeding expansion valve and how are they connected differently?

    Thanks

  2. #2
    Join Date
    Feb 2005
    Posts
    150
    Post Likes
    A none bleed expansion valve is a valve that will close completely, not to allowing the systems pressures to equalize. This helps prevent flooding the evaporator on the off cycle.

    A bleeding expansion valve does allow pressure equalization on the off cycle, were evaporator flooding is not a problem, and allows for a lower torque compressor for starting.

    Both valves would be connected the same. Only the internal parts are differant.

    These designs are for differant system applications. Changing valves on a system could cause the compressor to slug liquid, or a compressor starting problem.

    Why do you ask?

  3. #3
    Join Date
    Feb 2005
    Posts
    7
    Post Likes
    Thread Starter
    thanks,

    I often got asked and don't know

  4. #4
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Some non bleed applicatins will use the TXV as a solenoid because it will provide 100% shut off and in place of using a large solenoid, You can use a small one on the externally equalizer line to act as a pilot duty solenoid and slam the valve shut.

  5. #5
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    A non-bleed valve will do as the others say; i.e. not allow system equalization to prevent floodback to the compressor upon system startup.

    It is also thought that a system that does not equalize after shutdown will spend less time coming back into its nominal operating parameters after it restarts. IOW the compressor isn't spending a lot of time pulling the evap back down to design saturated vapor temp/pressure since the pressure in the evap at startup is more or less already there.

    Non-bleed TXV's will require a start cap and potential relay on a single phase compressor.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •