    Hold up I am not a serve tech I am a installer but I do know some service he ask what was a run capacitor & Start Capcitor was I told him I could be wrong that would not be the first time but if I am wrong then modern refrigeration and air condittionimg book is wrong because I looked it up in dictionary of techncal terms to make sure I was right were is NormChris he know everything he can tell us.

  2. #42
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    It depends. On a CSCR motor, the run cap is in the circuit connecting the start and run windings in series with one another.

    On a PSC motor the run cap is in parallel with the "start" and the "run" windings.

    Power is applied to the start winding through the start capacitor only until the switch (whatever form that might take) opens, then, the power is rerouted through the run capacitor. Actual line power is no longer applied directly to the start winding at that point, but current does flow through the winding.

    The run capacitor takes the "place" of the start cap, after the motor is at or near full speed. (Often called 75% of full speed.)

    And, eddy, I'm pretty certain that you do want to argue.


  3. #43
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Originally posted by framehvac
    Start Capcitor electrical storage device used to start and run circuits on many electric motors.

    Run Capacitor a device that dissipates heat generated by a motor.
    A run capacitor is the same exact thing as a start capacitor. It does the same exact type of work. It ONLY dissipates the heat from itself, which is generated as a side effect of it's constant charging and discharging. Nowhere in the Modern book, that I can see, does it refer to or describe the run capacitor as a "heat sink", which is what you infer with your second sentence.

    The capacitors charge up and discharge energy, adn, for the millionth time, simply shift the phase angle of the power being applied to the winding to which they are attached, for the single purpose of "straightening out" incorrect phase angles.

  4. #44
    Join Date
    Aug 2003
    Posts
    1,898
    Post Likes
    Nowhere in the Modern book, that I can see, does it refer to or describe the run capacitor as a "heat sink", which is what you infer with your second sentence.


    Modern Refrigeration and Air Condittionimg book 18th edition pg.1159 run capacitor at the bottom of the page.


    Run Capacitor a device that dissipates heat generated by a motor.


  5. #45
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

  6. #46
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Originally posted by framehvac
    Nowhere in the Modern book, that I can see, does it refer to or describe the run capacitor as a "heat sink", which is what you infer with your second sentence.


    Modern Refrigeration and Air Condittionimg book 18th edition pg.1159 run capacitor at the bottom of the page.


    Run Capacitor a device that dissipates heat generated by a motor.

    The newest copy I have is from 1992, and doesn't go to page 1159. I think Norm is going to tell you that that is wrong, also.

    Is that from the glossary?

  7. #47
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    No edition number listed on my copy, but it appears to be the 6th.

    Are you looking at "Modern Refrigeration and Air COnditioning" by Althouse, Turnquist and Bracciano????

  8. #48
    Join Date
    Aug 2003
    Posts
    1,898
    Post Likes
    condenseddave
    Professional Member

    So did you see it it is in the book this is a book that they use in hvac schools I think you know your sh!t but is the book right or wrong I think a teacher would take Run Capacitor techncal term on a test & I think that is what this guy is looking for.

  9. #49
    Join Date
    Aug 2003
    Posts
    1,898
    Post Likes
    No edition number listed on my copy, but it appears to be the 6th.

    Are you looking at "Modern Refrigeration and Air COnditioning" by Althouse, Turnquist and Bracciano


    Yes!6th edition time to update but if you have the 6th edition then I would say you know what you are talking about but in my book it does say that.

  10. #50
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Dave your beating a dead horse, The Run and start windings are never in series they are paralell with one point in common that would be C

  11. #51
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,461
    Post Likes

    Dave

    Just for your info -
    the shaded-pole & the resistance-start, induction run motors are the least torque producing motors of the single-phase class. That is because they do not use capacitors.
    The shaded-pole motor uses a 'ring' attached to one pole to create a very small phase shift, with very little torque produced. The RSIR motor uses a winding of small wire to produce a large resistance to accomplish a small phase shift ( haven't plotted an RL circuit in a long while ) but I might could if need be.
    Also, what do you think a cap-start motor is ??
    basically the same thing as a RSIR motor but with a cap added for better starting torque - with a centrifugal switch to remove it.

    And oh by the way, A compressor motor with a start & run capacitor operates with both caps in the system at the same time, but the start-cap is removed by the start-relay, leaving the start winding & the run capacitor in series together but in parallel with the run winding. The start & run windings are 'never' in series. Motor wouldn't work that way.

    Electrician for 30+ years

  12. #52
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Thank You BornRiding,

    Now that we have gotten over that hurdle,can we now move on to how it looks a lot like a three phase motor.

    Would someone please explain what a single phase to three phase converter does and what it does it with.

  13. #53
    Join Date
    Aug 2003
    Posts
    1,898
    Post Likes
    fat eddy
    Member

    Registered: Feb 2005
    Posts: 334
    Thank You BornRiding,

    Now that we have gotten over that hurdle,can we now move on to how it looks a lot like a three phase motor.

    Would someone please explain what a single phase to three phase converter does and what it does it with.



    I can't beleave you don't know that if you don't know then I am not goning to tell you.HaHa So just tell us?

  14. #54
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Do tell please,

    Enlighten me,

    I do know the answer very well I want someone else to tell him so that he might beleive it.

  15. #55
    Join Date
    Aug 2003
    Posts
    1,898
    Post Likes
    fat eddy
    Member

    Registered: Feb 2005
    Posts: 335
    Do tell please,


    Can I phono someone?No I will take my 50/50 so give me my 50/50.


  16. #56
    Join Date
    Apr 2002
    Location
    Battle Creek, MI
    Posts
    1,562
    Post Likes
    In my edition of MR&A/C,published in 2000, it does describe a run capacitor on pg. 1159 of the glossary as "A device that dissipates heat generated by a motor." This is clearly in error and should have been caught by the editors. What they are trying to say is that the run cap has to be built to dissipate the heat it develops since it is left in the circuit while the motor runs, as contrasted to a start cap which is only energized for a fraction of a second and therefore doesn't have sufficient time to heat up. This is explained in the text on pg. 268.

  17. #57
    Join Date
    Jan 2005
    Posts
    109
    Post Likes
    Capacitor law...all caps are wired to line voltage. All caps are wired to start winding.

  18. #58
    Join Date
    Jan 2005
    Posts
    109
    Post Likes
    Anyone believe that one?

  19. #59
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    That is a false statement Oil

  20. #60
    Join Date
    Jan 2005
    Posts
    109
    Post Likes
    Which cap. shell is plastic? Run or start?

Page 3 of 4 FirstFirst 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •