Thread: steam boiler

  1. #1
    heatseeker Guest

    Hmm

    Weil McClain boiler 68 series, costumer let fuel oil tank run to empty. went to check it out bled air from fuel line,changed nozzle & filter. Fired it up it worked fine,boss always wants to run several cycles on everything we work on to make sure everything is working right. Evetything tested good,done smoke test,draft test etc.


    Let boiler run for awhile while i was at lunch. Came back and the pressure relief valve had released some water onto the floor. had to replace the relief valve , fire the boiler again and got a puff of smoke when it fired.

    The rest of the day the thing would fire perfect and then the next time it would smoke again.Fire good , smoke,smoke,fire good. ???

  2. #2
    Join Date
    Feb 2005
    Posts
    11
    Post Likes
    Do a pump pressure test. sounds like your dripping fuel out the nozzle during shut down

  3. #3
    heatseeker Guest

    steam boiler

    done a pump pressure test,showed 120 psi & a vacuum test, still the darn thing will fire perfect one time and puff smoke the next

  4. #4
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    The relief valve has nothing to do with the smoke problem. That 15 psi relief popping should worry you. What is the steam pressure????????

    What was the vacuum cutoff and is this one or two pipe?

    Draft? Chimney, power or direct vent?

    Pump strainer?

    Actual combustion test results?

    Cad cell resistance?

    Need a lot more info.

  5. #5
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Weil McLain 68?? Does this have their old QB burner on it?

  6. #6
    heatseeker Guest

    steam boiler

    The smoke test showed about a 1,& the draft test showed 6.It is direct vent into a chimney,the steam presure is 18 but keeps trying to rise to around 20 psi,the pressure relief valve is rated 30 psi. The boiler runs fine but you still get that puff of smoke about every third fire up.

  7. #7
    heatseeker Guest

    steam boiler

    did not test the cad cell,but did't thing it would be the problem since this thing fires perfect sometimes and it runs good even after it fires with the smoke puff, Dave

  8. #8
    Join Date
    Jul 2004
    Location
    Odessa, FL
    Posts
    465
    Post Likes
    Draft should be closer to -.03. Also 18PSI in a steam boiler...that is a bomb waiting to go off. Steam should run at half a pound.
    How much is it an hour?

  9. #9
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Re: steam boiler

    Originally posted by heatseeker
    The smoke test showed about a 1,& the draft test showed 6.It is direct vent into a chimney,the steam presure is 18 but keeps trying to rise to around 20 psi,the pressure relief valve is rated 30 psi. The boiler runs fine but you still get that puff of smoke about every third fire up.
    First off, if this is a residential steam boiler, in a typical home, that pressure is dangerous. The relief on a residential steam boiler shouldn't exceed 15 psi. That 30 psi relief has turned that boiler into a bomb.

    The steam pressure should be no higher than 2 psi.

    The presssures you list are typical of hot water boiler pressures, and would be normal for hot water.
    Are you CERTAIN that this is steam????

  10. #10
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    If that is steam, and it's residential, either call your boss or the homeowner, and get them to turn that off NOW.

    Seriously. That needs IMMEDIATE attention.

    Smoke is the least of your worries right now.....

  11. #11
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Confused Uh, where did he go?

    Heatseeker, you out there??????????/

  12. #12
    heatseeker Guest

    steam boiler

    I'm back Dave need help, the draft pressure i quoted may have been wrong the company i work for has very primitive equipment, so that draft reading may have been wrong, this draft gauge is old and doesn't work right some time, Stupid question. When the needle drops to the right is this a negative or a positive reading?

  13. #13
    heatseeker Guest

    boiler

    The burner on this thing is called Blue Angel,this thing was installed in 1988

  14. #14
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Is it a Bacharach MZF or a Dwyer magnehelic?

    And, are you SURE that this is a steamer????

  15. #15
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Re: boiler

    Originally posted by heatseeker
    The burner on this thing is called Blue Angel,this thing was installed in 1988
    That's a Wayne. They set up differently than a Beckett.

    There is a "rebuild" kit for that burner still available.

    It's a piece of shit.

  16. #16
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Teh puffing might be delayed ignition, but I am SERIOUSLY worried that that boiler might really be steam. If it is, people's lives are in danger.

  17. #17
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Heatseeker

    Not trying to be a dick, but I an truly deeply worried about that boiler running at that pressure.

    Steam boilers are only rated at 15 psi. IF you pop a hole in that thing, and it drains down, dry fires, and then gets cold water dumped on it, the building will blow up and people will die. No kidding. Seriously.

    If you're not SURE that if it's steam or not, say so, but make sure that this thing gets checked to be certain, and soon.

    I'm not trying to scare you, just trying to impress upon you the gravity of the situation.

  18. #18
    Join Date
    Jan 2002
    Posts
    1,196
    Post Likes
    Step away from that boiler and get professional help. If you don't even know what you are looking at, leave it alone.

    This is really scary, or it is a troll.

  19. #19
    Join Date
    Jan 2002
    Location
    tip of the mitt
    Posts
    2,005
    Post Likes

    Heatseeker, although this is a wayne burner

    Beckett offers classes in Elryia,Ohio. Please check into this,it's really worth it.
    I have my own little world. But it's OK...they know me here.

  20. #20
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    key questions:

    What is the model number on the boiler?

    What is the model number of the limit control?

    What is the model number of the low water cut off?

    Noel

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.